So are you telling me that we don’t have to earth since it’s done at the substation. Where I live the power lines is medium voltage at 7200 volts then it goes to a step down transformer at 240 vac phase to phase after that it comes to me I have to bond it again. Dave I’m trying to understand
How many supplies are fed from each transformer?
Yes the star point is connected to earth at the substation, what happens after that depends on the type of supply. The resistance to earth of that connection is tightly regulated and will usually be well below 1 ohm.
The substation will usually have 11000V coming in and nominal 400/230 coming out.
For residential and small commercial supplies the substation will feed one, or usually multiple, distributing mains.
The distributing main is a large three phase cable running down the street usually underground or occasionally overhead.
Each single phase service is then jointed onto one of the phases of the distributing main, usually ever third house along a street will be connected to the same phase.
All connections of the neutral to earth are made by the power company. We are not allowed to connect neutral to earth in a consumers installation.
[automerge]1568409878[/automerge]
Dave I watched Pete999 video where the power company gives y’all 2 wires 1 being 240vac and a 0v wire which it seemed the 0v wire y’all get and y’all have to earth it, is that correct
The 0V wire is the neutral, we don't connect this to earth.
The confusion is coming in because that is presumably describing a TNCS or PME supply.