Discuss wholesalers mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
18
Im looking to put a supply out in a mancave, the earthing arrangement is tns. At the supply there is iscos installed so I was going to take a supply out of the iscos into a 40 amp DP MCB and run a 6mm T+E surface piped along an outside wall. I will be installing a 40A 30mA RCD in the mancave. My query is the wholesalers dont stock 40 amp double pole MCB's, I cant find anything wrong with what im planning in the regs.
The fact the wholesaler doesnt stock them has sorta through me a bit. Do I need to protect the supply cable with an RCD in the house aswell.
Thanks in advance.
 
T/E is not advisable outdoors. best use SWA. could start with T/e indoors and then switch to SWA in adaplable box. making sure that the armour is earthed, even if not used as cpc. RCD at supply end only needed if the first section of T/E is buried < 50mm deep in wall/s. you could start with a 40A S/P MCB into a D/P switch
 
T/E is not advisable outdoors. best use SWA. could start with T/e indoors and then switch to SWA in adaplable box. making sure that the armour is earthed, even if not used as cpc. RCD at supply end only needed if the first section of T/E is buried < 50mm deep in wall/s. you could start with a 40A S/P MCB into a D/P switch
point noted about the cable type. I will have to install a 3 module cu with a 80a DP MCB and a 40a SP MCB.
 
no. 40A single pole MCB, then into a 40A d/p switch. this give D/Pisolation for the exterior lghts.
 
It's not ideal to use a MCB at the house end of the cable. It may switch off at the same time as a lower rated MCB in the shed when a fault occurs. A switch/fuse, such as the one in my link, gives better discrimination, and will take a SWA gland direct.
too expensive and space my be an issue. I prefer this with a 45A fuse.:

1620159928358.png
 

Reply to wholesalers mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
572
Hi all, been reading around this and i have to admit ive quickly gone out of my depth as regards EV chargers. The charger in question is a...
Replies
18
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
890
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock