If you have primary and secondary it is likely to be isolating. Sounds like a site transformer.
 
Can you draw a diagram of the arrangement and post it?
I am unsure if you are asking

A rcd feeding primary side, will a fault on secondary fed circuit trip it.

B if you have an rcd on the primary supply, will a second rcd on secondary output still work.
 
As well as the issue of isolated or not, the question of the effectiveness of an RCD on the output of an isolated transformer is also dependent on how it is earthed (if at all).

Some transformers (e.g. shaver supply) result in an IT arrangement and an RCD is of little use, but a typical 110V site transformer is 55-0-55 with the centre earthed, and for that an RCD is going to work even though 55V to earth is usually considered safe enough not to need it.

Usually is not always!
 
Can you draw a diagram of the arrangement and post it?
I am unsure if you are asking

A rcd feeding primary side, will a fault on secondary fed circuit trip it.

B if you have an rcd on the primary supply, will a second rcd on secondary output still work.

Not the best diagram aha
 

Attachments

  • A8E58E62-273C-4E2C-9699-04D682323F38.jpeg
    30.1 KB · Views: 16
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?
 
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?
OK, so try answering a few questions first to see if you can deduce the answers:

1) Is the transformer you sketched isolating on not?
2) What path for current in a RCD trips it?
3) To answer question (a) is your answer to #2 normally present in this arrangement?
4) Your question (b) has several aspects:
  • What is your definition of "not work"?
  • How might two RCD in series fail to meet the IET regulation 536.4.1.4?
  • Returning to your answer to #2, is that present in your diagram for the secondary circuit?

My understanding is it wouldn’t work as it has a separate live and neutral. So to rcd protect it we’d have to put an rcd downstream and change the upstream to a time delay to comply with regs
 

Reply to Will an rcd operate in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi all I have seen a schematic drawing for a control panel recently where they (whoever drafted the drawings, designed the panel) show a RCD...
Replies
2
Views
501
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
352
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
327
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock