Discuss wiring a metal building in HI. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
I'm located on the East side of the Big Island, Hawaii. Due to the copious amounts of rain and the ever-present Sulphur gas from Kilauea Volcano which ranges from virtually imperceptible to close the doors and windows and wait till the wind changes direction. I've purchased a Steel Master metal building, 20' x 30' to be used as a part time garage and place to tinker and make stuff. I'm currently in my 15th month, waiting for the Building Permit approval from the county but that's another story. Because of the humid and occasionally corrosive environment, I would really like to run sch 40 pvc conduit, j-boxes and device boxes. I don't have a current NEC book but I believe the main issues are, different heat ratings for pvc than metal requiring de-rating the conductors and not installing pvc where it can be physically damaged. I plan on having HELCO run the aerial service drop to the end of the building: weather head, 2" ridgid mast to the Milbank, to the interior mounted 200-amp panelboard, then come out of that with pvc for all of my branch circuits. I also want come out of the bottom of the panel, into the slab, into a trench, alongside the domestic water H2O line (at least 1' distance between the two) approx. 80' into the slab for the house and mount a 100-amp sub panel in the house. I'm reluctant to go to the Planning Board with any questions because I think I'm close to getting permit approval, not that they've been much help in the past. I've also asked three different "electricians" and gotten three different answers. I fear the problem is they don't want me doing any of the work myself; potential money out of their pocket. Any thoughts of suggestions would be welcome. Oh, and as an aside, I retired from the Dept. of the Navy, civilian, 20 years as a Govt. electrician, and I didn't come here with enough money. But it's all good. I'm living in Paradise!
 
Great story. Different to the usual run of the mill stuff!

Our American member megawatt will probably be able to help you.
 
I'm located on the East side of the Big Island, Hawaii. Due to the copious amounts of rain and the ever-present Sulphur gas from Kilauea Volcano which ranges from virtually imperceptible to close the doors and windows and wait till the wind changes direction. I've purchased a Steel Master metal building, 20' x 30' to be used as a part time garage and place to tinker and make stuff. I'm currently in my 15th month, waiting for the Building Permit approval from the county but that's another story. Because of the humid and occasionally corrosive environment, I would really like to run sch 40 pvc conduit, j-boxes and device boxes. I don't have a current NEC book but I believe the main issues are, different heat ratings for pvc than metal requiring de-rating the conductors and not installing pvc where it can be physically damaged. I plan on having HELCO run the aerial service drop to the end of the building: weather head, 2" ridgid mast to the Milbank, to the interior mounted 200-amp panelboard, then come out of that with pvc for all of my branch circuits. I also want come out of the bottom of the panel, into the slab, into a trench, alongside the domestic water H2O line (at least 1' distance between the two) approx. 80' into the slab for the house and mount a 100-amp sub panel in the house. I'm reluctant to go to the Planning Board with any questions because I think I'm close to getting permit approval, not that they've been much help in the past. I've also asked three different "electricians" and gotten three different answers. I fear the problem is they don't want me doing any of the work myself; potential money out of their pocket. Any thoughts of suggestions would be welcome. Oh, and as an aside, I retired from the Dept. of the Navy, civilian, 20 years as a Govt. electrician, and I didn't come here with enough money. But it's all good. I'm living in Paradise!
It is fine to run PVC conduit and use PVC junction boxes. As far as the the de-rating the wire that applies for conduit on roofs where it gets real hot. You should be fine. As far as physical damage to the raceway that applies to flexible sealtite
 

Reply to wiring a metal building in HI. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Replies
3
Views
544
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
Good morning all. I have scanned posts and haven't found the exact answers I am looking for so I'd like to ask for a bit of advice related to my...
Replies
2
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock