Discuss Wiring diagram for a 3 phase motor on single phase supply in the UK Electrical Forum area at ElectriciansForums.net

M

Micklane

A customer has an existing application using 2 off, 4 pole contactor/relays of Brook Crompton make, model HR1310 and 3 capacitors of 200, 60 and 20 microfarads. The 3 phase motor is an English Electric, 4 pole with nameplate details - 2 HP, 400/440, star connected, (but the motor may be delta connected for 240 volts). This motor is on a lathe and the controls are inside a metalclad box with a start and a stop pushbutton. The supply is at 240V single phase from a 13A plug.

The fact that the relays are of Brook Crompton make, suggests that this was a proprietary method of this application.

I realise that this setup using discrete relays for the control is out of date, but has anyone got a wiring diagram for this unit? One of the relays is immediately energised when power is switched on, and I think the other relay should briefly switch on the start capacitor (the 200 microfard, I think), to start the motor from the start pushbutton, i.e. this relay is not retained.

The owner has replaced the relay for running, since it "was always energised" and the motor could only be stopped by switching off at the 13A plug. It appears that he has miswired the relay, since that relay energises but nothing else works!.

An inverter is an option, I haven't pursued this route but they are expensive, as is a single phase motor.

Regard
 
Emm you will not get a 3 phase motor to work on a single phase supply Do you mean how do you wire a single phase motor on to a 3 phase contactor overload setup
 
This probably isn't the same set up you have, it may help. It's the only way I've seen in person a 3ph motor running on a single phase supply.

3ca2512c.jpg

b2cb8db2.jpg
 
Emm you will not get a 3 phase motor to work on a single phase supply Do you mean how do you wire a single phase motor on to a 3 phase contactor overload setup
Not true, this existing application for a hobbyist in this case, is an older method of conversion using 3 capacitors and a start/stop pushbutton; and originally supplied by Brook Motors as I understand. Inefficient but practical at the time before inverters.

Regards
 
Not true, this existing application for a hobbyist in this case, is an older method of conversion using 3 capacitors and a start/stop pushbutton; and originally supplied by Brook Motors as I understand. Inefficient but practical at the time before inverters.

Regards
OK but never seen this elsewhere
 

Reply to Wiring diagram for a 3 phase motor on single phase supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
629
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
550
Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
263
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
797
Looking to use this brooks Compton motor as a replacement in an electric cement mixer. can anyone tell me if it is designed to operate off a...
Replies
2
Views
649

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock