Hi,

I’m not an electrician so seeking advice as to whether my requests were actions correctly or if I need to arrange for additional / remedial work to be done.

During the first fix of a renovation I told the electricians working on my project that I planned to put an office / studio in the garden at a later date & could they run something outside that would be suitable. They told me that they’d install an external socket and that any connection could be spurred off that for an office constructed at a later date.

I am now in the process of getting quotes for the studio and not sure if the external socket will be enough? The renovation isn’t quite finished so although it would be a real pain to run another cable from the fuse box it would be easier to do it now rather than later.

I attach pictures of the cables that are running to the outside as well as the external socket (this one OA036AG) . We would be planning to have a couple of 230v sockets (charging laptops etc) and some lights.

Would be grateful for any advice,

Nikki
A4D963AC-86C4-4AF4-83DE-22DC1BC5DF7E.jpeg

9214423B-B846-4E96-B327-A212037F1B75.jpeg
 

Attachments

  • 0A28BE7C-2B1F-4B79-B761-30235B308B76.jpeg
    291.5 KB · Views: 4
It depends very much on what you want to have in the office.

A feed off that socket is likely to be limited to 13A so OK for powering a decent amount of LED lights, a PC or laptop, and a single 2kW heater (not full 3kW). So quite small and limited, but if that is all you plan on doing there it is fine.

If you want a lot more (hot tub, several heaters, etc) it is going to need a dedicated feed and a lot more design information for sizing that.
 
Whether or not you can spur off of that socket depends on what the existing wiring an circuit arrangements are to the socket.
If it is an unfused spur off of a ring final circuit, which is what most external sockets would be, you cannot extend to your studio, unless you install the fused spur BEFORE this existing socket.
Looking at the size and quality of the building you are constructing, I feel it would be a mistake not to install a decent size feed (min 10mm2) direct from your electricity meter.
 
Thanks a lot for taking the time to reply, much appreciated.

I plan to have 4/5 double sockets, some led spotlights, 2 x wall lights and a heater.

I’m afraid I really don’t know if it’s a fused spur from a final ring circuit - the whole place was all re-wired and this external socket was done at the same time as that...

In any case it sounds as if I am likely to need more power than that provided by spurring off the external socket - but I will obviously ask a specialist to come and assess things.

Thanks again,

Nikki
 
Hi,

I’m not an electrician so seeking advice as to whether my requests were actions correctly or if I need to arrange for additional / remedial work to be done.

During the first fix of a renovation I told the electricians working on my project that I planned to put an office / studio in the garden at a later date & could they run something outside that would be suitable. They told me that they’d install an external socket and that any connection could be spurred off that for an office constructed at a later date.

I am now in the process of getting quotes for the studio and not sure if the external socket will be enough? The renovation isn’t quite finished so although it would be a real pain to run another cable from the fuse box it would be easier to do it now rather than later.

I attach pictures of the cables that are running to the outside as well as the external socket (this one OA036AG) . We would be planning to have a couple of 230v sockets (charging laptops etc) and some lights.

Would be grateful for any advice,

Nikki
View attachment 64886
View attachment 64884
Is the outside socket you want to spur off ofa spur already, or is it part of the RFC??
 
@Pete999 I'm sorry I'm afraid I don't know. The external socket has its own wire from the fuse box if that means anything?

Yes @loz2754 @westward10 I don't know why they didn't either, I definitely asked for it though, I remember the conversation as I had to ask them to explain what spurring was as it wasn't something I was familiar with.

To be honest it's not really surprising (although doesn't make it less frustrating) as there were quite a few things I asked for that they didn't do / did differently to how I'd asked for them to be done (socket placement etc.). I managed to get the main contractor to get them to change most of it to the way I'd asked but I had no idea that the external socket might not be enough until I started getting quotes for the work outside.

But hopefully I will be able to find a solution (or rather get another electrician who can!).
 
If there is a breaker in the CU (fusebox) that is labeled outside socket only, and this is true, then you can go on from it to your studio. Not even a fused spur is required, as long as the cable to the studio is of an adequate size for the rating of the breaker.
This would be fine if you were building a small garden shed, but I still say you'll eventually regret it if you don't give this place its own largish dedicated feed.
What is the rating of the breaker? (likely B16, B20 etc.)
 
For the sake of a few hundred quid , I would buy some 4mm swa and put in a dedicated 30a supply

you are spending thousands on a nice outbuilding , why skimp now

The outside socket might be wired in 4mm... We may find out...
 
i like working with 4mm swa and 30amos is plenty for most domestics

10-16mm is overkill for domestic office power
 
I'm not sure what I'm seeing in that picture. It looks like coils of cables with about 4 cables going into the wall from the coil.
Is the outside socket behind the coils?
 
I'm not sure what I'm seeing in that picture. It looks like coils of cables with about 4 cables going into the wall from the coil.
Is the outside socket behind the coils?
Sorry it’s not that clear is it! The outside socket is directly behind the wall with the wires on it - the kitchen is in now (well nearly - as you see) and the induction hob and a socket will be in this island bit, hence all the wires.
81B154C9-2627-45E2-97B7-2292F5B86A6B.jpeg
 
In that case, a 32A supply to your studio should be possible. Go on from the outside socket with 4.0mm2 or 6.0mm2 3C SWA to a small non RCD consumer unit in your studio.
Only downside, is that the RCD for the studio will be indoors on the main CU, so if it trips you will lose all power to the studio, including lights, and you will have to go indoors to reset it.
 
In that case, a 32A supply to your studio should be possible. Go on from the outside socket with 4.0mm2 or 6.0mm2 3C SWA to a small non RCD consumer unit in your studio.
Only downside, is that the RCD for the studio will be indoors on the main CU, so if it trips you will lose all power to the studio, including lights, and you will have to go indoors to reset it.
I'm surprised Brian that you would condone changing the size of the cable at the point of connection to the outside socket, not one person has asked if this outside socket is a spur or whether it is part of an RFC, apart from myself post 6, sorry for the disagreement to your reply.
 
If, as it appears to be, it has a dedicated 32A MCB feeding it then it should be at least 4mm cable and plenty capable of feeding the garden office. When all of the current work is done the completion certificate should confirm that, along with various other measurements that would allow the correct design of the office electrics.

The only possible issue is what @brianmoooore pointed out - the RCD protection is in the house's main CU (fuse box) and shared with other circuits. Not normally a problem, but an extra inconvenience if a fault does develop (compared to separate RCD).

For sockets and lights in a small office style arrangement you almost don't need a 2nd CU in the out building as the lights could come off a FCU (fused connection unit), but for all the cost of a CU it provides a handy place to isolate and test circuits, even if the MCBs in it have little selectivity with the feed from the house.
 
Thanks @pc1966 and @brianmoooore - and thanks in general to everyone for all the replies, I didn't expect to receive so much good advice in such a short space of time!

I note your points re the cable size / whether there are any other connections to the 32A MCB / RCD protection (annoying but not insurmountable). The completion cert is not yet done as there are a few things still to be connected up (kitchen appliances etc.) but will show this to whoever does the work outside once I receive it.

Obviously I will be getting a qualified professional for all the studio electrics but it does seem to make a difference in how seriously I am taken on site if I'm well informed (at least as far as I can be as a non-specialist). Just wish one of you guys had been my electricians in the first place!

Thanks again

Nikki ?
 

Reply to Wiring for garden office - can I spur off an external socket? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
313
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
763
Hi Gents, I am thinking about running some cables in the garden. The idea is to electrify the garden. My idea is to run some electrical cables...
Replies
10
Views
2K
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock