Discuss Wiring heater and thermostat advice please in the DIY Electrical Advice area at ElectriciansForums.net

qthisup

DIY
Reaction score
0
Hi - we have an inline heater for a vent system that appears to always be on. I believe the electrician may have wired it incorrectly with only a 2 core wire from thermostat to heater control board. Please find attached wiring diagram and photos of the heater control board and the thermostat, would someone be able to kindly confirm the correct wiring of thermostat to heater?
IMG_0843.jpgIMG_0842.jpgIMG_0841.jpg
 
Looks to me like the wire from terminal 12 is missing if jp1 is off
or wires 11 and 12 if jp1 is switched on.
 
Looks to me like the wire from terminal 12 is missing if jp1 is off
or wires 11 and 12 if jp1 is switched on.
Thats what I was thinking. JP1 switched on appears to enable the NTC10 which is the remote thermostat. Therefore terminal 11 to Out1 on thermostat and terminal 12 to In on thermostat?
 
Also Gnd and gnd1 need to be joined at remote unit.
 

Reply to Wiring heater and thermostat advice please in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all looking for some helpful advice I'm an Aussie so go easy on me, I have a good mechanical engineering head but first time plumbing and...
Replies
32
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
170
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
445
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Help please! Got this to use as a doorbell but unsure of specifics and wiring. If someone could maybe help with a diagram/specific parts or even...
Replies
11
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock