Discuss working out volt drop in the Industrial Electricians' Talk area at ElectriciansForums.net

D

darren1981

Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator
In the garage there is to be 2 power sockets and 1 lighting circuit with 4 florescent luminaries this will be connected to a small rcd cu with a 6A mcb for lights and 16A mcpvfor power there are also no ECP .
I am using a design current of 17.A 16A for the radial circuit which is the rating of the mcb and 1A for the lights rated at 0.25A each
so the swa cable Vd is 18mv/a/m so 0.018×17×20 =6.12v
lighting Vd 1.5 mm t/e 29mv/a/m so 0029×1×10 =0.29v
power 4 mm t/e 11mv/a/m so 0.011x16x10 = 1.76v

giving a total from supply to end of light circuit 6.41v
which is less then the max of 6.9v or 3%
And total for power of 7.88v which is less then 11.5v or 5% given
I know this is on the limit but providing new and upgraded swa to garage is a nightmare and if it's there would like to use

can anyone find a problem with this. Any help would be great
 
Why calculate for both circuits when you are only supplying 1 cable, calculate the VD for that cable that will be sufficient
 
what will the sockets be used for? if no heating appliances,welders, etc., then you'd be hard pushed to pull >10A
 
Also, you can calculate each circuit in sections if you wish - so if you have four light fittings along a radial circuit at 10m intervals, the first 10m is calculated at full load, the second at 3/4 load, the third at 1/2 load and the fourth at 1/4 load (assuming all loads are the same).
 
Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator
In the garage there is to be 2 power sockets and 1 lighting circuit with 4 florescent luminaries this will be connected to a small rcd cu with a 6A mcb for lights and 16A mcpvfor power there are also no ECP .
I am using a design current of 17.A 16A for the radial circuit which is the rating of the mcb and 1A for the lights rated at 0.25A each
so the swa cable Vd is 18mv/a/m so 0.018×17×20 =6.12v
lighting Vd 1.5 mm t/e 29mv/a/m so 0029×1×10 =0.29v
power 4 mm t/e 11mv/a/m so 0.011x16x10 = 1.76v

giving a total from supply to end of light circuit 6.41v
which is less then the max of 6.9v or 3%
And total for power of 7.88v which is less then 11.5v or 5% given
I know this is on the limit but providing new and upgraded swa to garage is a nightmare and if it's there would like to use

can anyone find a problem with this. Any help would be great


Looks generally OK. Not looked up the VD figures. A few comments:

I'd be surprised if you really have 10m of final circuit for the lights. Certainly it won't all be carrying the full load of the circuit. However, in this case, refining the calc won't make much difference.

Have you taken power factor into account with the lights? It's not much current anyway, but just for completeness.

Why are you using an RCD board in the shed when the distribution circuit is protected by an RCBO?

Why are using 4mm² for the socket circuit on a 16A MCB?

With this sort of question, it's always worth stating the earthing system in use.
 
It's suppled from a pme system
rcbo at supply end and rcd at garage end but over the top but it's not going to give any nuss tripping.
4mm fro radial (got in in the van )
 
What has PME go to do with RCDs at both ends ?
he is a trainee mate with 8 posts.

to op ask your mentor what they would recommend but you shouldn't be designing it yet because there are errors already and you might make a hash of it.

before you do this answer a couple questions first.

ccc of 2.5 swa,twin etc
why do we use rcd's?
why is having two rcd's in series a bad idea?

in a TT system what is the difference between the upfront rcd and a 61008?
 
Supply SWA connected in to switch fuse. RCD/RCBo's at the board!

Pointless having an RCD both ends unless the upstream one is S type. Not really necessary with PME?

Any thoughts on this anyone?

That is what I was getting at, the SWA does not need RCD protection on a TN system, two 30mA devices won't discriminate anyway, I was wondering why the OP brought PME into a (possible?) reason for the supply RCBO ?
 
That is what I was getting at, the SWA does not need RCD protection on a TN system, two 30mA devices won't discriminate anyway, I was wondering why the OP brought PME into a (possible?) reason for the supply RCBO ?
he is a trainee, i wouldnt be suprised if he is a first year

it sounds like a homework question, if it is its in the wrong section


he mentions mv/a/m on basic domestic circuits so its homework, why would you need to work this out when it gives you all that info in bs7671 and onsite guide if we wanted it
 

Reply to working out volt drop in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi I've a few questions regarding volt drop. Apologies if its a little longwinded but I'd like to get my head around everything. An example...
Replies
1
Views
1K
P
Hi guys. Those who don't know me I have recently started on my own. I am testing my understanding, re Volt drop. And trying to stick to one...
Replies
20
Views
3K
Its been along day, I've just finished off with looking around a big garden which has all sorts of electrical things going and would appreciate a...
Replies
31
Views
5K
Hawkmoon
H
Excuse how long winded this is but want peoples opinion: :angel_smile::frown2: Doing a basic shed install but would just like people...
Replies
11
Views
2K
Octopus
O
F
Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with...
Replies
9
Views
15K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock