Discuss Would a breaker be bad if it reads no voltage at breaker? The 50 amp gfci breaker for my hot tub is not reading voltage in the UK Electrical Forum area at ElectriciansForums.net

depends on whether there is voltage at the input side of the gfci. if not, then the fault is further back to the panel. could be a tripped breaker or a damaged cable.
 
The 50A gfci for my hot tub is not reading voltage.
There’s a couple of things that could cause that and one of them is are the wires actually in the screws on the breaker but you still should read the voltage. It also could be a bad breaker, try swapping it out with another breaker in your panel and see if your still not reading voltage and it don’t have to be a GFCI for test purposes. After your pull the breaker check the buss bar and see it has been heating up and reading voltage. Bottom line is the breaker could be bad.
 
These can 100 percent fail, with the switch "on" giving no voltage output. If this is the type that clips onto the busbars in the board, remove it, and just pinch the terminals so they clamp a little closer, they try it again, if still no voltage its bad. If it is a direct screw clamp connection on the feed side, just check to see the screw is tight and that you have voltage there if you do, then again it is bad.
 

Reply to Would a breaker be bad if it reads no voltage at breaker? The 50 amp gfci breaker for my hot tub is not reading voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
Hello, I had an electrician install a 100Amp subpanel which feeds a mini split. I addition I added a Homeline 50A GFCI breaker to power a shed. I...
Replies
9
Views
2K
Hi, My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and...
Replies
1
Views
888
Trying to connect a 50 amp inlet box to my Siemens outdoor combination panel 200 amp cutoffs. Can’t figure out where to insert the 50 amp breaker...
Replies
1
Views
850

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock