Search the forum,

Discuss Would you code a 60 amp main switch been fed from a 100 amp BS1361 in the UK Electrical Forum area at ElectriciansForums.net

I see your thinking now, so I won't code this.

Sometimes I need to stand back and look at what I'm seeing and thinking from a different angle.

Thank you for your advice.

Martin

Whether you code it or not is your decision.
When deciding on coding an observation you will find it helps to ask yourself the same questions I have done above. For C1 'what is the immediate danger here?', C2 'what is the potential danger?' for C3 'what improvement do I recommend/can this situation be improved?'
 
Well 230v is the declared single phase voltage throughout the country now even though nothing has really changed [apart from the network becoming ever more stretched to the limit] so that's what we have to base calculations on, I see what you're saying about the heaters though.
 
I have never seen the voltage at 230v, and am measuring everyday, the lowest I have seen it is 235v. Never seen 216v, but 250v yes. 315v but that was ug fault lol
 
Well 230v is the declared single phase voltage throughout the country now even though nothing has really changed [apart from the network becoming ever more stretched to the limit] so that's what we have to base calculations on, I see what you're saying about the heaters though.

That is not the declared voltage, it is the nominal voltage, something which some jobsworth in an office has written down and is impossible to implement. Nothing has changed because it cannot be changed, the whole country has substations with their output fixed at 250/433, there's nothing any jobsworth penpisher can do about that!
It doesn't change the basic physics though, If the stated power rating is at 240V you cannot just replace 240 with 230 in the calculation. The power dissipated will be less at 230V so the current which flows will be less.
 
Last edited:
Ironically the supply here was always 230V unlike the 220V in the south of Ireland and the 240V in Britain, and so harmonisation had no effect here!
 
That is not the declared voltage, it is the nominal voltage, something which some jobsworth in an office has written down and is impossible to implement. Nothing has changed because it cannot be changed, the whole country has substations with their output fixed at 250/433, there's nothing any jobsworth penpisher can do about that!
It doesn't change the basic physics though, If the stated power rating is at 240V you cannot just replace 240 with 230 in the calculation. The power dissipated will be less at 230V so the current which flows will be less.

Yes DECLARED as the NOMINAL voltage, only because the distribution network is so stretched and it gives them more leeway, I often see low to mid 230s here in Cornwall. And what's a penpisher ? :confused: :wacko:
 
Yes DECLARED as the NOMINAL voltage, only because the distribution network is so stretched and it gives them more leeway, I often see low to mid 230s here in Cornwall. And what's a penpisher ? :confused: :wacko:

If it has been declared as a nominal value then it is still only nominal! It has nothing to do with the **** state of the networks, the nominal voltage was changed to 230 by the penpushers in Europe, it was not changed to give anybody more leeway as the voltage has always been permitted to drop as low as 230.

It should have said penpusher
 
Yes I know, and of course it's purely coincidence that they can get away with a lower voltage- it can quite legitimately be under 230 now, the network is in lovely condition.
 

Reply to Would you code a 60 amp main switch been fed from a 100 amp BS1361 in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock