Discuss Ze at its Maximum Measurement in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I would say the question is are your required disconnection times met for the final circuits?
You do however have 30mA additional protection which will provide fault protection also.
 
Your final circuits need to meet max, and from DNO side that number gives 5 second disconnection for 60A fuse, if I recall correctly.
 
Readings for Zs at Cooker on 32A were 1.05ohms and sockets on 32A were 1.24 ohms. Both above the maximum 1.08ohms for a 32A RCBO.

Given the fact there is additional 30mA protection and theoretically 1667 ohms is the maximum value allowed given this would enable a 50v touch voltage, is this allowed? Or would DNO have to be notified?
 
When your Zs exceeds the max permitted you have to look at design first and foremost. RCDs will become fault protection rather than additional protection and the max Zs permitted should be recorded as whatever rated RCD is deemed necessary to meet those times.

However installing RCDs as fault protection to cover poor design is not acceptable. Goven what you have said then I don’t think this is down to poor design.

Are there any other reasons for RCD protection on all circuits?
 
I would be checking my dead test figures ....

Ze + (R1 + R2) = Zs

Some RCBO's are well known for giving higher figures....

Out of interest what was the Line to Neutral reading
 

Reply to Ze at its Maximum Measurement in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
275
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
479
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock