Discuss Zone 1 under bath tub in the Industrial Electricians' Talk area at ElectriciansForums.net

It changed when the byb came out its now zone one all the time now

I feel you may have misunderstood/read this part of the regulations Joe.

My BYB clearly states that - The space under the bath tub or shower basin is considered to be zone 1. However, if the space under the bath tub or shower basin is only accessible with a tool, it is considered to be outside the zones.

Conclusion Nothing has changed in BS7671 from previous to current AMD3.

:50:
 
. The OP is talking about a circuit external to the location but passing through it, and outside the zones, so no RCD required.
i am aware that the OP is talking about a circuit external to the location but passing through it.
It does not matter that it passes through the location outside of any zones, it still passes through the location.
It requires now in the 17th edition just as it did in the 16th edition, additional protection.
However the additional protection required now is solely by means of an RCD.
 
Last edited by a moderator:
i am aware that the OP is talking about a circuit external to the location but passing through it.
It does not matter that it passes through the location outside of any zones, it still passes through the location.
It requires now in the 17th edition just as it did in the 16th edition, additional protection.
However the additional protection required now is solely by means of an RCD.
Taken from the Stroma guide to 3rd AMD: Bathrooms - There is already a requirement for all low voltage circuits in a bathroom to be 30mA RCD protected. There is now a new provision requiring low voltage circuits passing through Zones 1 and 2 of a bathroom to be 30mA RCD protected.
 
Taken from the Stroma guide to 3rd AMD: Bathrooms - There is already a requirement for all low voltage circuits in a bathroom to be 30mA RCD protected. There is now a new provision requiring low voltage circuits passing through Zones 1 and 2 of a bathroom to be 30mA RCD protected.

Just looked it up. You're right.
'701.411.3.3 Additional protection by the use of RCD ... shall be provided for low voltage circuits
(i) serving the location
(ii) passing through zones 1 and/or 2 not serving the location.'

Can't see any specific requirement for cables passing through outside the zones.
 
Taken from the Stroma guide to 3rd AMD: Bathrooms - There is already a requirement for all low voltage circuits in a bathroom to be 30mA RCD protected. There is now a new provision requiring low voltage circuits passing through Zones 1 and 2 of a bathroom to be 30mA RCD protected.

Interesting - I must admit I thought it referred to any cable passing through a bathroom - didn't realise it was limited to within zones 1 and 2 only. Daz
 
Apologies, I have yet to obtain a copy of the 3rd amendment.
The pre amendment wording is: "Aditional protection shall be provided for all low voltage circuits of the location, by use of one or more RCDs having the characteristics specified in Regulation 415.1.1."

I was aware that many people believed this requirement only applied to circuits which served the location, and were unaware that it also applied to circuits just passing through.

I'm pleased that the IET have taken measures to clarify matters, though I am surprised that they have decided to limit it to only circuits which pass through zones.
 
Last edited by a moderator:

Reply to Zone 1 under bath tub in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
615
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
824
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
432
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi, I am after some advice please. I am a bathroom fitter and are in the process of installing a jacuzzi bath. All plumbed in and ready to test...
Replies
1
Views
503

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock