can I also assume that Pevvers has been in contact with you and told you exactly what he meant because I haven't heard anything from him.

And apologies for not getting back to you sooner, as I have been on a NEBOSH course all day, trying to improve my knowledge off my own back. Because sometimes you have to get out and do things to improve yourself in this day and age, as things can't always be expected to be handed to you on a plate... ;)
 
Last edited:
BS88 fuses above 200A also do not have their max Zs in the BRB, also MCCBs have no data. This doesn't mean they're not recognised, just that sometimes you have look through a wealth of manufacturers literature to find the details. Unfortunately the regs only have a finite amount of space available and can therefore not show every protective devices details, otherwise it'd be much much bigger!!

True but 5A is not a standard rating of BS1362 fuse. Only 3A and 13A are, which I would imagine is why they are not listed.
 
Last edited:
Ah yes, but still manufactured to a British Standard, so information will still be able to be found...

Sorry my original post probably wasn't very clear!

But yes, there should be no difficulty finding the information if the will is there.
 
Thanks Ian
I take it from your kind words that you must be Pevvers appointed spokesperson can I also assume that Pevvers has been in contact with you and told you exactly what he meant because I haven't heard anything from him.
And I still can't locate the 5amp rating for the 1362, I wouldn't have asked if I could. Usually the 99.9% of crrospondance is extremly helpfull

Happy days

No I'm not Pevvers spokesman, it was just the way you have replied to him was the reason why I posted it, if you try googling fuse manufactures you will get your answerafter sifting through them like I have had to do when I want information.
 
ok my understading IS bns1362 primaraly plugtop fuses (BRB appendix 1 p229) as such on a plugtop there there for appliance protection from overload and short circuit currents. They are rarely used (20+ years experiance i have never soon) as a circuit protective device and as such why would a Zs reading be required?
 
ok my understading IS bns1362 primaraly plugtop fuses (BRB appendix 1 p229) as such on a plugtop there there for appliance protection from overload and short circuit currents. They are rarely used (20+ years experiance i have never soon) as a circuit protective device and as such why would a Zs reading be required?

Maybe if you are using them in a fused connection unit from a ring. Then the 5A fuse could be used for disconnection instead of the MCB.
 
Right then, Mr Eddieb, after a simple search in "Google" (you may or may not have heard of it) with the term "BS1362 5a max Zs", I have come across (right at the top of the page), some information from another forum on exactly the same topic.

Please have a look here - IET Forums - BS 1362 5A Fuses - Max Zs and then realise how very your question was to answer.

If you haven't got the energy to click the link, then I will give you the important bit here.

From Graham Kenyon MIEE (a knowledgable fella) :-

"Had this topic a few months back.

There never will be any "max Zs for 5A BS1362" in BS7671, because there ISN'T ONE !!!

(This is because of the way the BS1362 standard is worded, NOT a fault of BS7671).

Therefore, if using a 5A BS1362 fuse, you must assume Max Zs same as Max Zs for 13A, and possible minimum fusing times (for inrush current calculations) of 3A"


(Mods - at least I am showing willing ;) )
 
Maybe if you are using them in a fused connection unit from a ring. Then the 5A fuse could be used for disconnection instead of the MCB.


If it was being used at an FCU then its overload protection for appliance only not the circuit. You dont take Zs readings at appliances its furthest point of circuit or mid point of ring.
 

Reply to ZS for a 5amp BS 1362 fuse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, can someone give me some advice RE completing a small works certificate for a fused spur coming from a ring final. 1) In part 2 of the AMD2...
Replies
35
Views
7K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K
Hi wondering if someone can advise me on something.. Im installing a few outdoor lights, will spur them off a ring via fused spur. question is...
Replies
2
Views
2K
Once again I am using the Engineering chat as I think my question is more theoretical rather than 'diy advice'. If I am misusing the forum...
Replies
17
Views
2K
I am helping a local football club who are having some issues with Zs being too high on the submain. They have the supply Henley blocked into a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock