Discuss Zs is lower than my R1+R2 in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
I’ve just changed a few lights for a customer and I rarely do testing so not very knowledgeable on it. I tested 3 lighting circuits.
1st circuit - Zs is 0.48 - r1+r2 is 0.55
2nd circuit - Zs is 0.75 - r1+r2 is 1.02
3rd circuit - Zs is 1.06 - r1+r2 is 1.55

All breakers are B type 10A BS en 60898

What’s your advice/opinion on this?

Thanks
 
As said above parallel paths is one explanation.
Other that curiosity I wouldn't worry as even the higher readings are well within the permitted max Zs for a B10 device.
Did you measure a Zs at the board too?
 

Reply to Zs is lower than my R1+R2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
7K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K
hello 1.is that acceptable if i do only Zs test last point of the lighting circuit and on scoket! instead of measure R1+R2? i can caluclate R1+R2...
Replies
18
Views
22K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock