Discuss R1+R2 and Zs calculate acceptable? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
hello
1.is that acceptable if i do only Zs test last point of the lighting circuit and on scoket!
instead of measure R1+R2?
i can caluclate R1+R2 ACTUALY!
ZS-ZE=R1+R2 is it acceptable to write the value on certificate?

2. as i know the maximum Zs by rcd (rcbo)protected circuit 1667 ohm!
but if the measured circuit is wery high value ,but not reach 1667 ohm ,then is it still acceptable ?

IM new to testing learning currently!
 
ZE is your external loop impedence measure at the point of origin

ZS is you highest measured earth loop impedence (usually at the furthest socket outlet)

So as you say ZS = ZE + RI +R2 or R1 + R2 = ZS -ZE

If you need the actual R1 and R2 reading induvidually it can be worked out on the basis that your R2 reading will be 1.67 times greater than your R1. This is due to the earth conductor being smaller than the phase and thus has a larger resistance.

For example if ZE measures 0.2 ohms and your maximum measured ZS is 0.734

Then R1 + R2 = 0.734 - 0.2 = 0.534

R1 = 0.2
R2 = 0.2 X 1.67 = 0.334

All that said these figures dont prove very much. A ring circuit needs to be tested as per the IEE Regs, which I could explain if you wish.

We do now have an R1 R2 reading but we havent proved ring continuity!
 
It depends on the installation. If you are doing a periodic inspection on a property that you have access to old test records for if there is no sign of any modifications and the Zs is as previously recorded it would be safe to assume that R1+R2 is as previous.

It is not good practice to always assume that Zs-Ze=R1+R2 as there may be parallel earth paths, like a copper gas or water pipe connecting to a boiler. If that pipe work was ever removed or altered the parallel path may be lost, and your Zs will rise.
 
also measured Zs also can confirm the conductor contunuity no? test instrument will sign that ,if any conductor not connected well!
if the plarity is not good then the rcd will trip anyway!
im i wrong?
 
A parallel earth path can exist on any circuit, I was just using the boiler as an example. Lighting may have parallel earth paths via supplementary bonding in a bathroom.

I tested a place the recently where someone had borrowed an earth from downstairs lights for a few of the rooms upstairs, if the downstairs lighting circuit was ever modified this could cause the upstairs lighting to loose its connection to earth and it could go un noticed.

It had been tested 5 years ago, but I didn't have the test results. Last guy to do an EICR had just calculated R1+R2=Zs-Ze I guess.
 
but in new installation is acceptable?for initial verification!
mi right?

For an IV, I would say, ensure that the cct is totally isolated from the rest of the installation and take a measurement.

Periodics, depends who you're working for! Sometimes it was a question of getting a Zs somewhere and a Ze and leave the rest to the company. It wasn't my name going on any certificates!
 
Not really, you should do the full tests, especially for IV.

What I have said above, applies to an IV just as mush as it does an old property with no test records.

If you have miss terminated one of your CPC's, or builder has struck a nail right through the center but missed the live conductors completely and you have a good parallel earth path you aren't going to notice.

And if you don't notice and next guy comes to test it in 10 years and he calculated as well from your results he isn't going to find it either. Then a couple years down the line the boiler is relocated and all of a sudden your circuit has no connection to earth.
 
I always calculate (R1+R2)+Ze for my Zs values on all tests. Zs-Ze isnt accurate enough for me. Including on a ring main.

Ill also Zs all sockets and random poibts on other circuits as im sampling just to make sure nothing stands out.

I was interested to read that GN3 actually seems to recommend this method over live testing for Zs now. Safer I suppose.
 
I was always under the impression that summing Ze plus R1+R2 is an acceptable method of establishing Zs.

However, doing the reverse and subtracting Ze from Zs to determine R1+R2 is not acceptable practice.

Agree on the accuracy point above, I'm increasingly finding that no trip Zs tests are giving strange readings when lots of LEDs on ccts, though I'm running an older tester.
 
agree with most. on a new installation, or part thereof, no circuit should be energised until after dead testing , inc. R1+R2, has been carried out to ensure that the circuit/s is/are safe to energise.
 

Reply to R1+R2 and Zs calculate acceptable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
886
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock