Hi All

Question:
on TNS/TNCS the max Zs on a 32 Amp type B MCB is 1.15 Ohms.
On a TT system it's 1667 Ohms (17th Edition page 50 table 41.5) (and earth electrode below 200Ohms)

Why is the Zs allowed to be so high on TT??
 
Basically because

1667 ohms = 50v / 0.03A

Where 50v is considered the `safe touch voltage` (could alternatively be 25v for more demanding requirements)

& 0.030A (30mA) is the I^n (the tripping current) of the RCD protecting the circuit.



So above equation would permit a Zs upto max of 1667 ohms & still achieve disconnection via RCD before voltage rose above considered dangerous level of 50 volts

As suggested, any & all line to earth faults in a TT will be cleared by residual current device as the earth fault path has too high an impedance (typically) to achieve required disconnection times via fuses/MCBs (or disconnection atall - check out your PEFC :eek:)
So, for TT, MCBs provide overcurrent protection only.

In TN systems we do interest ourselves in achieving low enough Zs for the breaker to trip on line to earth faults, as this is considered our primary `Fault Protection` & the backup of an RCD is considered `Additional Protection` - even tho any functioning 30mA would always trip before the MCB. :confused:

So when a low impedance suppliers earth is provided, fuses/MCBs offer both overcurrent & earth fault protection...

whereas with TT, the fuses/MCBs give overcurrent whilst the RCD takes over earth fault protection

Hope thats clear enough for you :)
 
Sorry to jump this thread! So do you put max Zs as 1667 ohms on electrical cert instead of 1.15 ohms for above circuit on a TT system?
 
Wanted to double check on this one as spark i spoke to with about 20 years more than me in game and a lot of testing and cert filling under his belt said no to this one!:D
 
So what do ya think he`d say if you told him that this is also the case with TN systems with 30mA RCD protection? :eek:

Cos it is ;)

Personally i put in BS7671 derived figures for TNs, but its equally acceptable to use the 1667 figure (assuming safe touch voltage of 50)

Perhaps he should rely less on what was relevant 20 odd yrs ago & try to understand how disconnection times can be achieved today?

p.s. just noticed you`re registered with NIC - don`t just take my word for it, suggest you give em a ring & see what they say (will be quite interested myself as i`m with Elecsa & already know their view is as stated above)

Perhaps your mate might believe the NIC ?

Al
 
Last edited by a moderator:
p.s. just noticed you`re registered with NIC - don`t just take my word for it, suggest you give em a ring & see what they say (will be quite interested myself as i`m with Elecsa & already know their view is as stated above)



Al
Yeah will do, As long as i dont get the nic tech guy that sounds like he is sitting on the loo while hes taking your call! :eek: And that did happen once :D
 
I had my NIC EIC annual visit last friday and asked him this exact question just to make sure I was doing it right. You do indeed put 1667 in that box according to him. That's good enough for me:D

EDIT:
He also said you should put the maximum Zs you find in the IEE wiring regs in for all other cases, rather than the one's found on the NIC EIC test sheet covers. A B32 for instance is 1.44 in there (If my memory serves me correctly) rather than the 1.15 found on the test sheet covers.
I think I need to get a second opinion on that one though
 
Last edited by a moderator:
I had my NIC EIC annual visit last friday and asked him this exact question just to make sure I was doing it right. You do indeed put 1667 in that box according to him. That's good enough for me:D

For the clarity of others reading this thread, you`re specifically talking TT here ?

He also said you should put the maximum Zs you find in the IEE wiring regs in for all other cases, rather than the one's found on the NIC EIC test sheet covers.

As i said before, use BS7671 derived max Zs values - don`t insert the 80% adjusted of the On-Site etc

A B32 for instance is 1.44 in there (If my memory serves me correctly) rather than the 1.15 found on the test sheet covers.

Nothing wrong with your memory :)

32A x 5 = 160A Ia (fault current required to trip MCB within 0.4 sec - for typeB would be x5 of In)

then

230v / 160A = 1.44 ohms ( Uo / Ia < or = Zs)

I think I need to get a second opinion on that one though

You have one ;)

or should that be two? :confused:

:D
 
Last edited by a moderator:
Well, the job in question on my test sheet was indeed connected to a TT. But I see no reason why that shouldn't be the case for ALL circuits protected by an RCD.
That said, any circuit on a TN-S or TN-C-S with a high enough reading to go over those found in BS-7671 would indicate either a very high Ze or an R1+ R2 that needed a good looking at. I'm sure it's possible, but highly unlikely.
Have you ever come across a 'sound' ring main with a Zs higher than 1.44?

Edit
Oh yeah, and cheers for the second opinion. My mind is settled:)
 
Last edited by a moderator:
Because earth fault protection is provided by an rcd the figure for maximum zs should be 1667 ohms
The figures for TN systems are not noted for TT
IT is worth recording the actual ZS of a TT system for future reference when a PIR is carried out
The rcd in TN systems is for additional protection
The max zs of the primary protectrion in a TN system by the MCB should then be noted
 
Thanks to all for the discussion and clarity on this question - by the way - I too am NIC registered and I did call the tech helpline and was told that the answer is........... 1667!

Cheers
 

Reply to ZS on a TT system - Help! in the Australia area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock