Discuss Zs on light circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

Tonyashby

Hi guys I am wondering if u could help me please on testing a lighting circuit. I know ze plus R1&R2 equals zs but on a ring I can plug a device in on my tester on trip lock and it gives me the reading. How and where should I do on a lighting circuit with test probes. I am fairly new to this and would appreciate the help. Many thanks tony ashby
 
You are looking for the highest reading on the circuit, therefore the last light in the circuit, but best to test at all lights. Earth and neutral on respective terminals at ceiling rose and the live probe on the switch live terminal, obviously will need light switched on.
 

Reply to Zs on light circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
607
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
799
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock