Discuss Zs over max zs in the Industrial Electricians' Talk area at ElectriciansForums.net

K

KNIPEX

Hi guys, done a test today on a ringmain circuit only 4 sockets but the zs was over the max zs as to bs7671.

now this was on a type c rcbo, so as its on an rcbo not mcb i believe this still complies.

if it was an mcb it would have to be changed to type b.

just wanted to double check.

thanks guys.
 
Why are there type c's on a ring final; are there lots of motors on the circuit? What's the Ze and how long are the legs from source to mid ring? I know!! question after question!!
 
Why are there type c's on a ring final; are there lots of motors on the circuit? What's the Ze and how long are the legs from source to mid ring? I know!! question after question!!

all the rcbo are spec as type c 32a 30ma. that usual mate on loads of jobs.

no motors that would be type d wouldnt it???

i say the legs to mid point abot 20m.

havnt got the ze to hand sorry.
 
all the rcbo are spec as type c 32a 30ma. that usual mate on loads of jobs.

no motors that would be type d wouldnt it???

i say the legs to mid point abot 20m.

havnt got the ze to hand sorry.

Normally type B, IMO cause it's on rcbo would say it complies
 

Reply to Zs over max zs in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
477
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock