Discuss Zs question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

B

bs7671

I have been asked to work out Zs,I have the Ze value and the r1 and r2,however I cant remember if there is a temp correction factor once I have found the right circuit breakers on table 41.3.I thought it was (r1+r2)+Ze+1.2? Im not entirely sure can anyone help?
 
Sort of right, 1.2 is the correction factor used when circuit designing. This is to give worst case scenario when conductor temp rises to 70c.
 
I think its supposed to be worst case so 70 degrees.To be honest I dont really understand why its not already corrected in the regs,instead of being abient temp
 
Its on a college madeup installation and we have been asked to calculate Zs but I think they want to catch us out thats why I am unsure of these correction factors.I know Zs=(r1+r2)+Ze but how and when does the temp correction thing come in to play???
 
Zs from the BRB would be the max reading for that circuit breaker in order for it to operating in time (ie 0.4 sec), however when taking these readings into account you should also take into consideration allowance for temp factor or use the rule of thumb of 80%.

Take your maximum allowed Zs and multiply by 0.8.

Is this what you mean?
 
Its on a college madeup installation and we have been asked to calculate Zs but I think they want to catch us out thats why I am unsure of these correction factors.I know Zs=(r1+r2)+Ze but how and when does the temp correction thing come in to play???

You don't correct your readings - your Zs is your Zs.....that's it.:)

The maximum figures from The Regs need to be corrected to allow for conductor operating temperature - so you multiply these figures by 0.8 and compare to your Zs.

The OSG figures are already corrected.;)
 
If you are designing a circuit and you want a design figure of Zs you use the mill ohms per meter values from OSG or GN3.
These are based on a temp of 20 degrees so you x them by 1.2 which converts to an equivalent reading at 70 degrees.
Now add this to your Ze and you have a design value of Zs which can be compared to max values in BS7671 which are at 70 degrees.
 
Is this on a ring or a radial?

Have you been asked to check the suitability of the calculated value? - If not i would think you are looking too deeply with regard to temperature correction. If yes then temp correction for the values in the brb are needed.
 
You don't do any correction to the Zs reading its self ever. THe corection is the regs book Zs figures need to be multiplied by 0.8 as they are cold values and once in service temp shopuld rise which will increase resistance and make a borderline acceptable instalation over the limit and possibly not disconect in time.

You can use your onsite guide for the corrected values to save you working it out as its already been done.
 
You normall use the correction factor for designe and currrent calculation etc if you are to find the Zs and know the R1 R2 and the Ze then its Zs = Ze + R1R2
 
Last edited by a moderator:
because you are measuring Zs at ambient temp. which is anywhere between 40deg.F and 80deg.F in this country. designed operating temp. of the cable is up to 160deg.F. convert that to foreign temp. comes to 70deg.C. hence the correctin factor
 
big difference here with upper and lower case letters. i can see why people get confused.
 

Reply to Zs question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
605
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
893
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock