Discuss Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

pushrod

Just wondering if everyone actually does a Zs test when filling in a schedule of results. In the OSG it says that you can measure it or calculate it by addition. I appreciate the different value stuff, just thinking it is a lot easier and quicker to be adding 2 figures together than taking things apart and getting your test meter out again.

Cheers.
 
i think calculation is the way to go, as it gives you the worst case scenario. IE, the ZS reading might come in ok, but only because of some supplemantary bonding somewhere giving a better path to earth. In a few years, when the bathroom is changed, and the bonding is removed because it is no longer needed, then you have affected the protection of you original circuit that you measured ZS on.
Also it reduces the need to work live, as EAWR regs state: you should only work live where it is not reasonably practical not to do so.

I predict a good debate on this one!
 
Last edited:
I measure when practical...but calculate for RCBo's as they always trip and calculate most of the time on lighting circuits,as most light fittings are not exactly Zs tester friendly....and even if you do manage to connect the probes the ******* 6a type B mcb pops out so you end up calculating anyway.
 
Someone always told me skip whatever test you want but if I find out you skipped the ZS test I'll sack you!

so always measure
 
I always measure one reason being if you have a faulty mcb or main switch in the installation with high resistance accross the device then the only test that will pick up this problem is a measured Zs.
 
From what i understand, it is acceptable to calculate Zs on a PIR, but not on a new or altered installation.

And how would you do that?:)


I vote for 'measure it' - especially if your only reason for not measuring it, is that you are too lazy to get out of your van and get your meter out :p
 
Ive got to admit, i didn't think about the loop test being the only one that tests the MCB (for resistance anyway). Thats a good point. I suppose that when youve done a lot of testing that you get to know what results to expect on a R1+R2, so that my earlier point about a Zs being misleading is null and void.

Happy to be educated!
 

Reply to Zs testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
881
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Replies
14
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock