Yes, you would never get 0.08 Ohms by enquiry.

The earthing conductor size is not an issue as regards Ze/Zs.

What is the type of the BS 3871 devices?
 
So you have 2 DB's with exceeded maximum Zs values.

Are these DB's much more remote or supplied by smaller CSA distribution circuits?

I'm really asking if this is down to poor design or cpc continuity faults on the distribution circuits in question...
 
Hi Knasher
Max Zs for 63amp 3871 mcb is 0.76 Ohms. with your Ze at 0.08 even if you uprated your main earth conductor too 16mm it wont make a differance to the high readings you have on some of the Diss board's. Check the connections off the Glands if it is on SWA's, corrosion on the armouring will draw the readings down. Use a P-Nut lock nut with a suitible supplementary to the earth bar on both ends will help.
 
It's a BS 3871 type 2 60A !

I make it a maximum of 0.55 Ohms tabulated, 0.44 Ohms at 80% value????

It's so important to get these figures right as the o.p. could (rightly or wrongly) use them in his diagnosis!
 
Found a bit more info from PIR guys and it includes: absence of supplementary bonding in places (been given code 1, which seems a bit bit extreme - wouldn't it be code 2?). Also, mentions poor connections on some ring final circuit patresses in certain offices. Another point mentioned is main bonding being terminated at sub distribution boards and not MET. All of these things could affect Zs couldn't they? Excuse my ignorance.

One final question for IQ electrical, can you tell me how you got your Zs figures - i've looked in GN3, OS guide and BS7671, applied rule of thumb etc but am none the wiser. Can you enlighten me. Cheers again everyone!
 
Yes, the type 2 trips at up to 7 times it's rated In current so from Ohms law, you get 230/420

That's 0.55 Ohms, 80% value of 0.44 Ohms
 
Found a bit more info from PIR guys and it includes: absence of supplementary bonding in places (been given code 1, which seems a bit bit extreme - wouldn't it be code 2?). Also, mentions poor connections on some ring final circuit patresses in certain offices. Another point mentioned is main bonding being terminated at sub distribution boards and not MET. All of these things could affect Zs couldn't they? Excuse my ignorance.

One final question for IQ electrical, can you tell me how you got your Zs figures - i've looked in GN3, OS guide and BS7671, applied rule of thumb etc but am none the wiser. Can you enlighten me. Cheers again everyone!

Code 1 for absence of supplementary bonding?
What were the locations lacking supplementary?

Connections to back boxes are imperative with conduit/trunking being used as the sole cpc-is this the case?
That would be a code 2 on my report.

All of those points can have an effect on Zs however in my experience , it's most likely down to the length of the distribution circuit or undersized cpc in the distribution circuit.
 
might be clutching at straws here, but, occasionally, you might fing a high resistance between the earth bar and the metal box in which it is mounted. if there is no fly lead between them.
 
Last edited:
It dont say in PIR where supplementary bonding is lacking - and its a pretty big building to explore, but still can do. As re. checking connections at back boxes, again thats easy enough. As re. length of circuit too long or under sized cpc, whats the most simple solution? install bigger cpc do you reckon?
Finally, thanks for shedding light on how you got Zs values for 3871 type fuses - didnt have a clue thats how you got figures! Cheers malcolmsamford too (havent checked out link yet but will do).
Is there any logical sequence to approaching problems like this or is it down to years of experience?
 

Reply to Zs too high at distribution boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
481
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
548
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock