Discuss Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

b=5x c=10x d=20x
zs = nominal voltage/Ia (current causing automatic disconnection) x0.8
examples of making disconnection times with various mcb types
eg b32
b x 5=160 230/160=1.43 x 0.8 = zs max of 1.15ohms
eg c20
c x 10=200 230/200=1.15 x0.8 = zs max of 0.92ohms
eg d16
d x 16=320 230/320=0.71 x 0.8 = zs max of 0.57ohms

c and d type breakers are used for circuits with high inrush currents

ive gotta get out more!
 
b=5x c=10x d=20x
zs = nominal voltage/Ia (current causing automatic disconnection) x0.8
examples of making disconnection times with various mcb types
eg b32
b x 5=160 230/160=1.43 x 0.8 = zs max of 1.15ohms
eg c20
c x 10=200 230/200=1.15 x0.8 = zs max of 0.92ohms
eg d16
d x 16=320 230/320=0.71 x 0.8 = zs max of 0.57ohms

c and d type breakers are used for circuits with high inrush currents

ive gotta get out more!

That's a great formula but would it still apply to bs88 fuses?
 
max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)

What gives you that idea??

Zs = Uo ÷ Ia is basic ohms law (R = V ÷ I).

Zs = Earth fault loop impedance -- Uo = Nominal voltage -- Ia = Current causing operation of the protective device in the required time

The 0.8 is a rule of thumb. The max Zs values in BS 7671 are at a cable operating temperature of 70°C but the cable won't be at that temperature when you take a Zs measurement, so you multiply the values in the BRB by 0.8 to account for the reduced temperature of the cable.

Ia is taken from the time/current characteristics graphs/tables in Appendix 3 of the BRB.

That's a great formula but would it still apply to bs88 fuses?

So yes, it does apply to BS 88 fuses. It's just easier to work out for 60898 and 61009 breakers because it's just 5 x In (type B), 10 x In (type C) and 20 x In (type D).
 
Last edited by a moderator:
Soooo - Smiffy is right then.
So yes, it does apply to BS 88 fuses.
Obviously, Ohm's law applies to everything but -
It's just easier to work out for 60898 and 61009 breakers because it's just 5 x In (type B), 10 x In (type C) and 20 x In (type D).
...there is no one value which applies throughout the amperage range of BS88s to calculate the maximum Zs for each.
 
Soooo - Smiffy is right then.
Obviously, Ohm's law applies to everything but -...there is no one value which applies throughout the amperage range of BS88s to calculate the maximum Zs for each.

No. What Smiffy said is that Zs = (Uo ÷ Ia) x 0.8 cannot be used for anything but 60898 and 61009 breakers.

max Zs= U0/Ia (x0.8) only works for B C D mcbs 60898 rcbos 61009. (table 41.3) makes life easier to work out max zs without looking it up... fuses i look up. ;-)

Uo ÷ Ia is how max Zs values are calculated no matter what the protective device.

Have a look at the time/current graph for BS 88 fuses on page 247 of the BRB. Let's say you have a 32A fuse.

For a disconnection time of 0.4s you need a fault current of 220A. Zs = Uo ÷ Ia (230V ÷ 220A = 1.04Ω). Now compare this with the value in Table 41.2 on page 48.

You then multiply this value by 0.8 to account for the reduced temperature of the cable -- 1.04 x 0.8 = 0.83Ω. This is your maximum measured value.
 
Yes, I know but smiffy's thread is about the fact that you don't need the graphs for 60898s because the relationship between Ia and In is linear,

i.e. 5, 10, 20 for B, C, D respectively.

This is not the case with BS88s and, indeed, other fuses.
 
Yes, I know but smiffy's thread is about the fact that you don't need the graphs for 60898s because the relationship between Ia and In is linear,

i.e. 5, 10, 20 for B, C, D respectively.

This is not the case with BS88s and, indeed, other fuses.

He didn't say anything about not needing the graphs.

What he said in post #75 was the formula for calculating max Zs "only works for B C D mcbs 60898 rcbos 61009". This simply isn't true.
 
Last edited by a moderator:

Reply to Zs values? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
795
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
774
Hi All, Can anyone help with calculating a Zs value for the fuse described in the title. The fuse sizes in Fig 3A3(c) of the 18th edition wiring...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock