Discuss Zs what if in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Right where I was going with this was, suppose a 4mm radial has been extended with 2.5 on a old 30a fed elect OPD and the efc at the original radial end is ok but at he extended end it the efc is lower much lower, then the table for a 32A (board change involved) the Zs drops of the scale, I know why it will not trip and I cannot for the life of me think how i thought it should with a low EFC, beer probably who knows, now for the time being I have whacked a 20 on the circuit but its a big radial 21 sockets on it 3 hotel rooms I know the logical thing to do is rip out the 2.5 or ring it back to the board but would it make any differance if I went with a32 as it,s now RCd'd and a shed load of bonding was done to ECP,s

thoughts anyone
Pict
 
if the 20A OCPD holds, and the Zs is within limits for that device,leave it at that.
 
A little confused at what your asking but.

If you have extended a 4mm radial in 2.5 cable your ZS is going to be higher than at the original socket due to reducing the csa and extending the lenth of the cable.

If your EFLI test is now too high for the OCPD to disconnect in the required time 0.4 secs (TN) system then you need to do something about it. You say a RCD is fitted on the circuit so you max ZS could be 1667 ohms but I would be dead testing and making sure the R1 + R2 was acceptable for the cct in question making sure there are no faults or high resistive joints etc!
 
Right where I was going with this was, suppose a 4mm radial has been extended with 2.5 on a old 30a fed elect OPD and the efc at the original radial end is ok but at he extended end it the efc is lower much lower, then the table for a 32A (board change involved) the Zs drops of the scale, I know why it will not trip and I cannot for the life of me think how i thought it should with a low EFC, beer probably who knows, now for the time being I have whacked a 20 on the circuit but its a big radial 21 sockets on it 3 hotel rooms I know the logical thing to do is rip out the 2.5 or ring it back to the board but would it make any differance if I went with a32 as it,s now RCd'd and a shed load of bonding was done to ECP,s

thoughts anyone
Pict

Why dont you improve the circuit so it does comply is that not what this is all about I was called to a job with a high Zs turned out there was a poor main earth contacted DNO who came 2 months later (because there was a RCD) and put a good earth in now Zs complies
 
To clarify this is how I understand it:-

If the Zs meets disconnection period spec, then it will trip the CB within the alloted time period when a Live to Earth fault occurs (eg: 0.4s). However, if it can't meet it, then there must be additional protection from an RCD, to eliminate the risk of the earth becoming live because of a high ZE. This is the basic TT protection mode.

For normal ADS without RCD protection, the disconnection time is of course mandatory.
 
There's a big difference between a TN and a TT system!! The use of an RCD on a TN system is for ''additional protection'', It' shouldn't always be considered a cure all, for covering a wiring circuit that doesn't comply with required Zs when it can quite easily be made to comply. Whereas, on a TT system, especially in UK, it is the prime and only protection for earth faults

The use of RCD devices for cure all situations seems to be, becoming the norm in the UK. Get the fundamentals right first, before applying RCD additional protection
 

Reply to Zs what if in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
764
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock