Hi guys, doing bit of revision here. What is the correct answer to give under exam conditions to this question? State why Ze-Zr cannot be used to accurately determine the value of R1 + R2? Could it be something to do with number of connections within the circuit under test, possibly a loose connection etc which would then give a higher Zs reading? I'm sure there must be a more obvious answer. Thanks
 
Hi guys, doing bit of revision here. What is the correct answer to give under exam conditions to this question? State why Ze-Zr cannot be used to accurately determine the value of R1 + R2? Could it be something to do with number of connections within the circuit under test, possibly a loose connection etc which would then give a higher Zs reading? I'm sure there must be a more obvious answer. Thanks


What's Zr when it's a home?
 
Driverman

parallel paths can make an enormous difference to the final Zs. The difference of an order if the Ze is appalling (which it often is, TT wise).

so for example, you may get a Zs of 6.4 Ohms for a circuit with a Ze of 122 Ohms and an R1+R2 of 0.67 Ohms.

how could Zs - Ze ever be a useful measurement, except in how useless it might be....do you see from the example above?

the bonds to the water pipe and gas pipe in the example above massively reduce the Zs.


In fact, some properties that are TT can happen to be connected via a water main to another nearby property that is TN.... Thus producing even more incredulous results (like a Ze at the earth rod of say, 34 Ohms but the socket circuit reads 0.34 Ohms for its Zs).

s.
 

Reply to Zs - Ze in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock