Discuss zs? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
allo folks hope u's r well, my seaward multifunction tester has a function wen testin earth loop impedance that gives u earth fault current and then u push a button and it also gives u short circuit fault current so record which is the highest for ze ok but wen testing zs for eg on a lighting circuit does the same principle apply do u record the highest of the two readings or should it just be one or the other? thanks in advance for the replies!
You shouldn't need to record any fault current for a final circuit, this will be determined by whether your measured Zs is below the max permissible by BS7671:2008.
So only line to earth reading needed,
many thanks yer a star lol
Reply to zs? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Electrical2Go - Megger MFT Deals!
Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
I would appreciate some opinions on the following situation...
I have been asked to comment on an EICR for a local community resource (church hall...
Can someone explain this to me?
The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.