thanks lads he was questioning why some of the test sheets he was given had codes given to high zs readings i was trying to tell him that there on rcbos and the max value becomes 1667ohms ha ha sorry i started
 
trying to explain to a client this but havent got books with me please someone refresh me were does the 50v come from this formula


zs for an rcd = 50v divided by 0.03 (30mamp) = 1667 ohms

The value of 50 V relates to the typical current levels that cause ventricular fibrillation in the heart of a human being and the typical resistance of the human body in 'normal' conditions. Apply V = I x R to these values and the result is the touch voltage. Theoretically the average person in normal circumstances should not die as a result of providing an electrical path between a metal part whose touch voltage is limited to this value and earth.
 
and you should be using the Zs values for the MCBs, not the cure-all RCD. the only time a RCD should be used for fault protection is on a TT install where nobody's arsed to get a decent Ra value.
 
yes i totally agree tel in my opinion its very un profesional to just add an rcd or rcbo to compensate a high zs reading you should investigate why your zs reading is high but napit put it in there mag that its perfectly acceptable and im looking at it right now
 
And who the hell are Napit for FFS? The only reference you should be taking any notice of is BS7671 and it's GN's/ An article in a magazine isn't worth the paper the mag is written on!!

Think about this, ....Why bother with ADS Zs values at all, on any installation if a 30mA RCD device has been provided?? At the end of the day, RCD's on TN systems are still classed (as far as i'm aware) as ''Additional'' protection, not ''Sole or main'' protection....
 

Reply to zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K
Hi everyone I asked my assessor about touch voltage and he was not keen on explaining properly and gave me a rough answer which made me think...
Replies
32
Views
5K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
892
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
432
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock