Discuss Surge protection devices (SPD) in the UK Electrical Forum area at ElectriciansForums.net

Not sure if you intended to reply to me Pete, but my point was replying to the comment earlier about height not affecting risk of lightning strike. Which it does.
No Mate it was just that your's was the last post, so I added my answer to it, wasn't questioning your post in any way, sorry if it caused any misunderstanding, if it did it was unintentional.
 
You can have two structures side by side with one taller than the other but there is no guarantee it will not strike the shorter over the taller one.

No, there's no guarantee as such, but the odds are higher for the taller building. To take it to the extreme, it's very unlikely a bungalow would get struck next to the Eiffel Tower. And don't say yes, that's because there isn't a bungalow there :)
 
No Mate it was just that your's was the last post, so I added my answer to it, wasn't questioning your post in any way, sorry if it caused any misunderstanding, if it did it was unintentional.

No worries at all mate.
 
No one on this forum is experienced with fitting SPD's and can answer any of my questions?

Do I need switchfuses or isolators? Why fused at 63a on a 20a circuit?

Please!
 
Hi guys, hopefully someones going to be able to point me in the right direction here.

We do a lot of work for a small retirement home locally that has recently decided to fit lightning protection. We've pretty much been strong armed into fitting SPD's on behalf of the lightning firm (LF). Being honest I don't have a great deal of experience with them and tried to sidestep the job. No such luck!

The lightning firm(LF) are supplying SPD's, but have supplied little further information. What they have provided seems inconsistent and vague. IMO they don't really seem to 100% know what they are talking about.

1.We have a 3 phase SPD to be fitted at the main intake position. There is a 3 phase DB here, but it has no spare ways. LF have said we need to split the tails and fit a 3 phase switchfuse isolator before connecting to SPD in adjacent enclosure.

2.We have 2x SWA cables running external around the building which we are told need SPD's at the load end. These supply a 3 phase washing machine and a 3 phase cooker (20A each). LF have been pretty vague here and sometimes use the word 'isolator' and sometimes 'switchfuse' and don't appear to know the difference. They want us to cut into the SWA before the existing appliance isolator and fit a 63A switchfuse (or isolator - who knows). This would isolate the SPD.

I'm not sure why 63A has been specified?

I'm not sure if I need to fit a switchfuse or an isolator? I'm not even sure what would stop someone turning it off by accident?

If I cut into the SWA at the load end I'm going to need to double up the cables in the supply side of the isolator - doesn't seem like the greatest design?

Can anybody offer some help/point me in the right direction here. I don't like just blindly following instructions that don't make sense to me.

Cheers

I did some research on domestic SPDs on behalf of my mother-in-law after the overhead 4 wire supply in her street was struck by lightning which damaged her skybox, TV and washing machine.

MK do some sockets but they mainly deal with voltage spikes and noise and when they are called into action the internal varisters or neons lose some or all of their 'life'. The socket for example has a cartridge which has to be replaced - I cannot remember if their is any indication that it needs to be swapped for a new cartridge. There are Consumer Unit modules too but these I seem to remember do have a flag to indicate they need replacing. I consulted MK Technical and they said the devices are not promoted to protect against lightning.

Anyway, this preamble is to say whatever SPD is fitted one needs to think about a regular inspection routine for some kind of flag that the device is still functional or not. Or, whether as a matter of course they must be replaced periodically.

My M-I-L thought the cost/benefit of SPDs in her home did not stack up.
 
Last edited:
No one on this forum is experienced with fitting SPD's and can answer any of my questions?

Do I need switchfuses or isolators? Why fused at 63a on a 20a circuit?

Please!

For your question in bold - I will deal with the second question shortly.

Please see the installation instructions for the PSD device you mentioned earlier:

https://library.e.abb.com/public/ba7860c5a8624189a51df9d903c2460a/ESP 415XXX Series ii 12.11.12.pdf

where at paras 4.6 and 4.7 it says:

4.6 Isolation It is good practice to be able to isolate or disconnect the ESP Protector from the supply. The means of isolation should therefore be installed in the connection to the ESP ProtectorThe supply to the entire distribution board should not be switched off on many computer power supplies and other critical loads. (see 4.7 - Fuse connecting leads).

4.7 Fuse connecting leads The connecting leads to the phase/live terminals of the ESP Protector should be fused. This is to protect the connecting leads in the event of a short circuit. The fuse to the ESP Protector (FSPD) should be lower than the upstream supply fuse FS by a sufficient enough factor to ensure fuse discrimination. As a general guide a factor of at least 2 could be used (FSPD ≤ 0.5 FS), where the maximum fuse to the ESP Protector required is 250 Amps (if the supply fuse is 500 Amps or greater). Refer to the fuse manufacturer’s operating characteristics to ensure discrimination, particularly where an installation includes a mixture of types of fuse, or of fuses and circuit breakers.

There are also important instructions on keeping short the cable lengths to the SPD via the isolator and fuse. So switch uses are ideal to provide isolation and over current protection in one and thereby keep cable runs as short as practical.
 
Last edited:
'Why fused at 63A on a 20A circuit'. You are referring to SPD protection for the 2 SWA supplues. You mntion the load they supply but not the size of their OCPDs. The guidance is provided in para 4.7 above viz (FSPD ≤ 0.5 FS) - so knowing the OCPD for each SWA supply you can calculate the fuse size to protect the wiring to the SPD.

That's how I read it - but I think having done the calculations and decided on cable sizes I would contact Furse technical department to confirm. Contact details are at the bottom right of the installtion instructions.
 
I forgot to mention, use cabling;

a. of csa equal to at least the 2 SWA's csas;

and

b. the largest you can fit into the terminals for the intake SPD.

You want to reduce skin effect and resistance/impedance of the branch off to the SPDs.
 
Further to my #36 - the guidance para 4.8 actually says a minimum of 16mm2 multistranded. Note well 4.9 and 4.10 about binding the cables together as well as keeping them short.
 
Thanks marconi. Reading through those instructions actually gives slightly more detail than the hardcopy ones I received from the firm doing the lightning conductors.

The SWA supplies are both 6mm 4core SWA with 20A OCPD. Why would they then specify 63A switchfuse or isolator?!

Ive also been wondering if I need to fit a switchfuse, or if I could fit an MCB in the same enclosure as the DIN rail mounted SPD. This would keep the tails to the SPD shorter and obviously keep the costs down to my customer.
 
Thanks marconi. Reading through those instructions actually gives slightly more detail than the hardcopy ones I received from the firm doing the lightning conductors.

The SWA supplies are both 6mm 4core SWA with 20A OCPD. Why would they then specify 63A switchfuse or isolator?!

If the upstream OCPD is 20A then the SPD can have a lower OCPD as stated in the installation instructions. Some form of isolation of the SPD is required if one wants to avoid turning off all power while servicing the SPD. If this is not an issue then the SPD can share the isolation provided for the cables and loads.

Ive also been wondering if I need to fit a switchfuse, or if I could fit an MCB in the same enclosure as the DIN rail mounted SPD. This would keep the tails to the SPD shorter and obviously keep the costs down to my customer.

OCPD for SPD must satisfy Fspd less than or equal to (0.5 x Fs), where Fs is upstream fuse or MCB, to provide discrimination. Fspd is providing short circuit protection for cabling to SPD.

The guidance allows you to do what you suggest; see paras 4.1 and 4.2. An advantage of installing it external but close is you do not have to turn off all power to maintain the SPD. The advantage of including it within DB is cables are shorter and SPD connected closer to intake.

Better informed now, you can have a discussion with the client on what he wants and why and how you propose to install the SPDs and why. Time for me to handover to electricians to resolve the niceties of installation. :)
 
Last edited:
It makes no difference.

You may need to read up on step leaders and streamers :)

Just a bit of banter...and it is accepted that lightning can hit a person,stood next to a high building,so,random is nature...

The fitting of a conductor,increases the probability of creating a streamer,which increases the odds,that it will make contact with the last step leader...don't shout at me,blame the scientists ;)
 

Reply to Surge protection devices (SPD) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
491
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
837
Following the tragic tale from @telectrix about lightning damage to phones and modem leading to a serious loss of beer money I decided to take a...
Replies
0
Views
773
Hello! I'm struggling to find an answer to this question online. I'm new here btw - I'm a DIYer with a physics degree Currently when my fridge...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock