Hi Guys,
I have a dining room with 4 spotlights and a living-room with 6 spotlights. Both are switched seperately with dimmer switches. However, when I try and dim either the lights dim really quickly and go off. I have to try and turn the switch when they are off and turn back on again to try...
Right guys got a 2way intermediate sscenario the 3 switches need to be dimmers (the dimmers are the issue)and dimmable lamps in the fitting
anyone suggest a particular make lights are all spotlights 22 in total split in 4 zones so minimum load could be 30 watt
looking at the Kosnic route anyone...
Hi, I'm new to the forum.
I have a domestic installation with; 14No 35watt lv lamps= 490 watts.
controlled by 5No 105va 'Mode' leading edge transformers = 525Va
I am trying to dim the circuit with a Richmond (now Zano) Grid 700 rotary dimmer...
Just fitted four kosnic 5w dimmable led gu10 lamps in my bathroom switched via a dimming pull cord, however when dimming nothing happens for a few seconds then all of a sudden they dim right down to nothing very quickly!
Am I right in thinking there may not be enough load of the dimmer to dim...
Greetings.
Apologies if this is a stupid question.
Say you wanted to install some garden lights and you decided on 12 Volt lighting because there were kids around etc.
Now say you wanted to dim them and you wanted a dimmer that was close to the lights IE outside.
Would it be possible to dim...
Hello,
I want to build into a lighting system a programmable dimming system which will smoothly dim the (standard) lights from 100% brightness to 50 % brightness over a period of 3 minutes, and then after a 10 second delay fade them back up to 100% over 3 minutes at which the lights should stay...
Has anyone ever managed to get LED's to dim using a dummy resistor?
You know when you fit a few LED lamps and the wattage amounts to about 30 Watts and hence too low for a standard dimmer.
I hear placing a dummy resistor in parallel with the LED load is the way to do it but can't find any...
Does anyone know the best solution on how to dim 4 x 7w dimmable downlights? Ive been looking at low load dimmers but they look pretty rubbish amongst the flat plate ive installed in the rest of the house. I'm hearing things about load resistors and would like some info on these if anyone has...
scott01
Thread
black
dimmer
dimming
lamps
led
please
problem
solution
their
One of my customers have asked me if they can recommend a dimmer that will work with "E27 T5 Quick start
11W CFL -460Lm".
Below is an email they have sent me.
Is there anyone here that has a good understanding on dimmers?
"The nightmare we are having is how we make these dim.
A single...
Hi I have just got a job in a big community hall. Complete refurbishment. Now they have asked for track lighting for the stage. On it they have 2 100w floods and 5 100W spot lights. Now all they want to control this is a 1gang dimmer switch.
Am I right in saying just any dimmer switch will be...
Hi Chaps,
Hope someone can help me with the following.
Have got a couple of wall lights on a standard rocker switch at present, with 2 x low energy lamps. These come to less than 40watts in total.
Customer want to put a dimmer in that is rated from from 40w - 300w.
Sure I've heard before...
Hi Guys,
Got a client looking for some alternation intelligent lighting solutions. Was going Lutron but he seen this. Lots cheaper and seems a doddle
to install and program.
They called Wise Dim
Anyone had any experiences with this brand and product?
Always cautious with new brands last thing...
Hi guys,
Recently installed a 12kW electric shower for a customer.
Customer has called me back because the lights dim quite noticeably every time he uses it.
Took some readings at the CU Main switch. Shower off = 248V, shower on = 236V, a voltage drop of around 12V (although still in...
puranah69
Thread
aus
dimming
lighting
lights
shower
using
voltage
voltage drop
volts
Fitted two 2 foot fluros for a customer but he now says they are too bright. Are there any cheap ways of successfully dimming them? I read that a dimmer switch will work to about 50%, turn on full power and once its fired up turn it down, has anyone tried this?
Thanks
Jon
Can someone give me simple explanation (Do not too technically) about how lighting dimming module works for Forward or Reverse phase? If any other link that I need to refer, please advise..
Your cooperation on this matter is highly appreciated.
Thank you.
Regards
Hi All,
A friend has just mentioned that when they turn their living room light off (a class 1 fitting with 3x 60w lamps controlled by a 1 gang, 1 way switch switch) the flourescent light in the kitchen goes off for about 5 seconds too then comes back on. Its controlled by a 1 gang, 1way...
Been ask to fit 2 L.E.D. light fitting the customer has asked about having them on a dimmer switch. Anybody know if this is possible and if so would it require special switch or driver?
Hi Guys -
I'm trying to find the best solution for this -
It has been wired recently but the installed 1000w dimmer has blown. This is on a single metal back box. The dimmer controls 3 big chandeliers switched altogether. Total load of each chandelier is: 480w. Total load altogether is...
Unswitched
Thread
aus
controller
dimmer
dimming
remote
resistor
these
Hi all. I'm new to this forum but have read some posts and found it very interesting.
I recently bought an electronic dimmer for my 12 V halogen lamp but I'm confused at how to properly connect it. The box where the line comes in is incredibly small and the dimmer's connection scheme is not...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.