Hi ALL
Have to install a Condenser unit on a roof in the nxt couple of weeks the length of run is around 50M the unit FLC is 24A will be Reference method E on Try for most of the run 4mm swa can take 41A table 4D4A and 6mm can take 53A. Just need some advice regarding VoltDrop
As this is...
I bought an old Craftsman table saw (circa 1982) a couple months back and today the motor stopped turning, instead it started just sitting there making an electrical buzz. I've got it apart and all the connections and stuff looked good, so I broke out the multimeter and measured the input...
Just been flicking through and table 7.1 to enable final circuits to be installed without calculating voltage drop has one of the criteria as
ii)The final circuit is connected to a dis board or CU at the origin of the installation
Just seeing that I understand this and the reasoning behind...
What does anyone think the maximum period between period inspection on holiday cottages should be?
Guidance note 3 is not too clear. I'm sure there are many installations which don't drop into the catagories as detailed in Table 3.2
My best suggestion is "Restaurants and Hotels", or...
The regs give a table for non delayed RCD's and circuits under 32A, how do you calculate max Zs if there is a delayed RCD or if the circuit is over 32A?
Hi all,
This is my first post on this forum, so please be easy on me.;)
We currently have new Merlin Gerin consumer units installed within Aberdeen College, and looking at table 41.3 b the eli readings should be 0.72 minus rule of thumb. This fails most of the existing circuits. When i...
KiltedSparky
Thread
earth
existing
impedance
loop
loop impedance
max
rcbo
readings
system
table
How do we calculate voltage drop on a ring final sockets only, Given the length of the circuit is 40 meters the cable is 2.5mm so therefore the amp per meter is 18, the mcb is 32 so is it 40 x 18 x 32 / 1000 = 23.04 but thats more than 5% = 11.5. Do we not use the mcb for socket outlets as we...
hogan
Thread
aus
cable
circuit
length
maximum
table
voltage
voltage drop
volts
Hi everyone
Would be really grateful for your help on this.
I have my 1st NICEIC assessment on Monday (am bricking it) - anyhow I only have an old table & I need one like you get on the back of the proper NICEIC pads - the most up to date table.
Has anyone got one they could send me so...
daz24
Thread
aus
earth
earth fault loop impedance
fault
help
help please
impedance
loop
loop impedance
max
needed
niceic
please
table
value
Hi Guys,
Here is a handy 17th Edition Loop Impedance Table.
This table gives you a direct comparison with your Zs tests results and is calculated @ the 0.8 Rule of Thumb figure.
Enjoy! :)
Warren