spraffers

hi guys, im fitting a 10.8kw mira sport max, i have read various threads on this and i think 10mm cable is suffice but the problem is at the moment my cable runs into the old cooker fuse on an old fusebox which is 30a.

I know i need an rcd fitted, it is wire through an isolator switch.
Can you please advise what i need to fit? eg rcd etc
 
25mm cable direct to cut-out fuse.:27: that'll solve the volt drop. why such a ridiculous size shower? a 7 kW gets you just as wet.
 
hi guys, im fitting a 10.8kw mira sport max, i have read various threads on this and i think 10mm cable is suffice but the problem is at the moment my cable runs into the old cooker fuse on an old fusebox which is 30a.

I know i need an rcd fitted, it is wire through an isolator switch.
Can you please advise what i need to fit? eg rcd etc

Seeing as your profile says you are a carpet fitter, i suggest phoning an electrician would be a good start.
 
10.8kw shower.
30A fuse how old do we need.

old cooker fuse on an old fusebox which is 30a.
i need an rcd fitted, it is wire through an isolator switch.

GET HELP ON SITE DO NOT DO THIS YOURSELF.
 
You will need the shower installation certificated anyway, so call in an Electrician to start with, not the fire service after you put 47 amps on a 30 amp circuit.
What do think of carpets fixed with panel pins or thumb tacks, dumb, so take advice with electric regulations, on the way that it must be done !
 

Reply to 10.8kw shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
298
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
932
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
585
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock