spraffers

hi guys, im fitting a 10.8kw mira sport max, i have read various threads on this and i think 10mm cable is suffice but the problem is at the moment my cable runs into the old cooker fuse on an old fusebox which is 30a.

I know i need an rcd fitted, it is wire through an isolator switch.
Can you please advise what i need to fit? eg rcd etc
 
25mm cable direct to cut-out fuse.:27: that'll solve the volt drop. why such a ridiculous size shower? a 7 kW gets you just as wet.
 
hi guys, im fitting a 10.8kw mira sport max, i have read various threads on this and i think 10mm cable is suffice but the problem is at the moment my cable runs into the old cooker fuse on an old fusebox which is 30a.

I know i need an rcd fitted, it is wire through an isolator switch.
Can you please advise what i need to fit? eg rcd etc

Seeing as your profile says you are a carpet fitter, i suggest phoning an electrician would be a good start.
 
10.8kw shower.
30A fuse how old do we need.

old cooker fuse on an old fusebox which is 30a.
i need an rcd fitted, it is wire through an isolator switch.

GET HELP ON SITE DO NOT DO THIS YOURSELF.
 
You will need the shower installation certificated anyway, so call in an Electrician to start with, not the fire service after you put 47 amps on a 30 amp circuit.
What do think of carpets fixed with panel pins or thumb tacks, dumb, so take advice with electric regulations, on the way that it must be done !
 
I have got a Mira sport max 10.8kw.

Yes it does get you wet like a 7kw, i can turn my one of full whack and my hot water comes out fast not a trickle like a 7kw.

Its a very good shower, I've got it on a 50A with 10mm cable.
 
use 10 mm cable providing the run is within the regs a 10.5 shower draws a lot of current-- the board needs to be able to handle it a 45 amp breaker or fuse would do the job
btw ignore the childish posts
 
Well i have a 4.2or 4.7KW (can never remember which) shower over here in my flat and the water volume/pressure is more than adequate as is the the water temperature. Never had one in any of my own houses, never had the need. 10.8 KW just sounds totally ridiculous to me, just in running costs alone, especially if you have teenage daughters. ...lol!!
 
can anyone remember the early electric showers?
the element was visual in a see through plastic enclosure 6kw maybye
i installed one for a freind ( a scouser) his son used to spend far too mutch time in there doing what young lads tend to do
 
use 10 mm cable providing the run is within the regs a 10.5 shower draws a lot of current-- the board needs to be able to handle it a 45 amp breaker or fuse would do the job
btw ignore the childish posts

He's a carpet fitter.
If you fitted your own carpet with half a clue of what your doing and no underpinning knowledge do you expect an excellent result?
Now turn the tables. Its an accident waiting to happen. How can he test his install to make sure its fit for use apart from getting a spark in? He may aswel get him/her in to do the lot.

I don't mind it when advise is given but it looks like a free training Q+A! Would you ask a brain surgeon questions in the hope of removing a brain tumor?

(Unless he is training to become an electrician and just working as a fitter to put bread on the table)
 

Reply to 10.8kw shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
558
At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock