Search the forum,

Discuss 11-12 volts reading across line and earth in the UK Electrical Forum area at ElectriciansForums.net

S

Sting Ray

trying to trace an earth fault in a friends home today after the RCD in the single ring main suddenly and persistently started tripping
why might I see 11 to 12 volts across line and earth on some sockets?
are there any tips regarding finding the earth fault? have broken the ring and disconnected all sockets and i am working my way along the ring reconnecting one socket at a time until the fault reappears
 
why might I see 11 to 12 volts across line and earth on some sockets?
Is this with the circuit live or isolated?
are there any tips regarding finding the earth fault? have broken the ring and disconnected all sockets and i am working my way along the ring reconnecting one socket at a time until the fault reappears
Have you got a mega tester?
 
To restate:
I see 11 to 12 volts across line and earth and a very low insulation resistance at 500V test voltage between line and earth
I know there is a short circuit somewhere and I have cleared all but two outlets on the ring so the ring is presently configured as a radial with the last part of the ring dead ie not connected to the main board or the incoming ring cable
I was curious about why the 11 to 12 volts appeared, nothing else
 
... why might I see 11 to 12 volts across line and earth on some sockets?

To restate:
I see 11 to 12 volts across line and earth and a very low insulation resistance at 500V test voltage between line and earth
I know there is a short circuit somewhere...

I was curious about why the 11 to 12 volts appeared, nothing else

Okay the way I read this is you're actually worrying about two different faults here. Firstly there's the low insulation that was causing the RCD to trip. Secondly there's a mysterious 11-12 volts appearing at some sockets between the L and E.

Just ignore the 11-12 volts between the L&E, chances are it's a meaningless reading because you're using a tester with an extremely high input impedance which is over sensitive. Concentrate on finding the extremely low insulation problem between N and E.
 
i hope you're not reading the MFTs battery volts that appear on screen when the MFT is powered up.
 
Start the fault finding technique either loose cable or damaged cable by screw etc break the ring main down until you find it.

Good luck can be a full in gruler it you could get lucky,

I once found that after British gas had put some pipes in the ring main randomly tripped turns out they had snagged a cable with the new nails they out in to floor boards and if some one walked on them it would trip too ages find can't beat the best in the business
 
Where has this trend for measuring voltage to do fault finding come from ?

I have noticed quite a lot of fault finding questions being posted, real,induced and phantom voltages are noted, then used to try and trace insulation and continuity problems
Does the training reflect this method these days or is it just the "in" thing to do this
 

Reply to 11-12 volts reading across line and earth in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock