hello all, does anybody know what sort of power factor 110v transformers deal with. would it be a standard 0.85? i want to know what kw output i'd get out of a 3.3kva tranny before i buy it. ta
 
You need to be careful here as a 3.3KVA tx will only deliver the maximum 3.3KVA for around 5-10mins before shutting down.

The continuous rating of a 3.3KVA tx is around half of it's maximum rating i.e, 1.65KVA for a 3.3KVA one.

Also depends on the nature of the load supplied by the tx & efficiency etc. etc.
 
trafos are just rated in VA

you'll get up to 3.3kw max depending on the pf of connected loads

as said they can be 'tool rated' (intermittent) or continuous
 
You need to be careful here as a 3.3KVA tx will only deliver the maximum 3.3KVA for around 5-10mins before shutting down.

The continuous rating of a 3.3KVA tx is around half of it's maximum rating i.e, 1.65KVA for a 3.3KVA one.

Also depends on the nature of the load supplied by the tx & efficiency etc. etc.

I’m confused…. Why?

OK I know things are cheap and crappy now, but 50% down rating seems a bit much.
 
from experience a 3.3kva tranny is usually rated 3.3 intermittent(approx 30 mins) or 2.5 kva cont.there is info on them usually from maker but thats generaly what I find.
 
I suppose my confusion is down to I’ve only put them in for permanent installations.
Only ever managed to damage one with overload, and that was done deliberately to show the effects to an apprentice. He had a fire fighting lesson thrown in for free!
 
As phil d states, read the manufacturers data before you buy!! There is a big difference in the continuous and intermittent rating on these site tool use Tranny's!! Having said that, is this what your talking about, or a permanent pukka type transformer, ...They are completely different animals!!! lol!! The let's say proper transformers, are a much heavier and sturdily built affair, than the building siteTool rated jobbies!!
 
I’m confused…. Why?

OK I know things are cheap and crappy now, but 50% down rating seems a bit much.


All site tool transformers (which is what I assumed the OP was referring to due to the 3.3KVA stated rating) are only rated at the maximum rating for a short period of 10-15mins. Continuous rating is always declared to be half of the maximum, by the manufacturer of the tx.
 

Reply to 110v transformers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Hello everyone. I'm in training but we haven't seen transformers or how they work yet. I have a transformer here I'm trying to figure out. There...
Replies
7
Views
1K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock