  1. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Dad has an old 1361 cartridge fuse CU, 16th edition so lights etc aren't RCD protected. It's Wylex, but I couldn't tell you the model.

    Gonna be changing some lights in the bathroom from batten to downlights, 701.411.3.3 says I need RCD protection. I've told my Dad it's probably easier and better for him to get a new board (me doing it, it's only gonna cost him materials), but I wondered if it was possible to get an RCBO to retrofit to this board - anybody know?

    Thanks,
     
  2. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Assuming it is an old Wylex Standard board then no.
     
  3. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Cheaper and better in the long run, to swap to a RCBO board.

    How many circuits and I'm guessing you won't charge dad for your time?
     
  4. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    No it's not that type, it's a typical 16th edition plastic CU with 1361 holders instead of MCBs, house was built around 2000 (my understanding is 1361 boards were very common on new builds in 2000 and 2001, must have been a dodgy deal gone on somewhere).
     
  5. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    I would put a rcd s/fspur out side bathroom and alter the lights
     
    • Like Like x 1
    • Agree Agree x 1
  6. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Of course not haha, about 8 circuits. Think I'd just go split load if he did upgrade.
     
  7. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Do the 1361 modules unscrew from the busbar.
     
  8. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Haven't had the cover off yet, but they look like this so I'm guessing they slot in to the rail like you would expect an MCB to.

    s-l1000.jpg
     
  9. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Why?

    A 10 way populated AMD3 board with 8 RCBO's is about £120.00 - a far better solution now and in the future when a fault occurs.......
     
    • Agree Agree x 1
  10. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Is it? When I put RCBOs in mine it was closer (I think above) the £200 mark, and that was using a budget brand.

    Just checked SBS prices (which I think are really reasonable) and that's £180 for 10-way, 8 RCBOs, VAT included.
     
  11. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    how many led down light are you putting in!
     
  12. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    4, not that it bares any relevance...
     
    • Like Like x 1
  13. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    for the cost of rcd s/fuse spur and alterations in the loft
    best guess tops £75 including led lights & fittings and your labour for free!
     
  14. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Yeah just been looking through an old Wylex catalogue and it shows the 1361 modular units you have in your pic, NSB range. A new NHX rcbo should fit but as they are compatible with NSB but it might be tight in the board.
     
    • Like Like x 1
  15. D00DY_T00DY
    Offline

    D00DY_T00DY Gorilla Whisperer Electrician's Arms

    Location:
    UK
    I believe BG are the cheapest in terms of rcbos(around the £15 mark per CB) not sure on prices of an unpolulated board but it's £120 for the Circuit breakers alone. Id imagine the board would be £100?

    Could you not fit an rcd board before the main board thus protecting all circuits on an rcd. Not ideal if there is a fault.
     
  16. buzzlightyear
    Offline

    buzzlightyear Electrician's Arms

    Location:
    star command
    hightower post a pic of the board !
     
  17. Murdoch
    Offline

    Murdoch Electrician's Arms

    Location:
    Woking
    Not an option......
     
    • Agree Agree x 2
  18. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Will do, heading to his tomorrow to do some other work so will be sure to grab a picture tomorrow
     
  19. telectrix
    Online

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    borrow a wylex RCBO from local wholesaler. try it for fit. if no fit, return to supplier.
     
    • Like Like x 1
  20. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    I don't know why, but since you posted that something in my mind said "I've got a bloody Wylex RCBO in the box sitting in the back of my van". Not sure if it's 20A or 6A though, time to go check...
     
    • Like Like x 1
  21. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    B16 but at least I have one to try for fit. Don't fit Wylex and forgot I had it until Tel prompted me.
     
  22. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    I'm with you buzz, fit a local RCD FCU. That said, if were my family, I would install a nice shiny new A3 CU. I picked up an MK 8 x RCBO CU for £120 a few months ago. If you do it now hightower, you won't have to put in an earth rod and AFDD's that you'll have to do for the 18th :)

    PS I've only managed to retrofit one RCBO into an older CU, unless you use a lump hammer and water pump pliers.
     
    • Like Like x 2
    Last edited: Jul 3, 2017
  23. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Was there last night, but far too busy to get a photo. I'll upload as soon as I think on to take one.
     
  24. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    That's a particularly [email protected] suggestion. Don't forget the division of circuits regulation (you know, single point of failure and all that).
     
    • Like Like x 2
  25. bigspark17
    Offline

    bigspark17 Electrician's Arms

    Location:
    wales
    What make and where do you get that?

    Maybe we should only discuss prices in the arms tho? ;)
     
  26. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    MK are supplying them at that price zone, if you have an account with a wholesaler, which most members of the public don't have ;)
     
  27. D00DY_T00DY
    Offline

    D00DY_T00DY Gorilla Whisperer Electrician's Arms

    Location:
    UK
    Tin hat on

    What about a split load board then? Does each half fail since their on one rcd? ;) :D

    How about a little garage board with a b6 for the lighting?
    Seen loads when someone's installed a new cooker/shower with old rewirable fuses what are am3 garage boards? £30-40?

    Or probably the best option of an rcd spur outside the bathroom
     
  28. hightower
    Offline

    hightower Electrician's Arms

    Location:
    Durham
    Just to keep everyone in the picture, I eventually installed his downlights. When I looked in the back of the van I had a spare enclosure and RCD so I put that in the garage and diverted the upstairs lighting circuit through it.
     
    • Winner Winner x 1