Taking a old storage heater off the wall for my brother who would like a single socket in its place.
It has it’s own circuit in the fuse board (b16 breaker)
I know a little about electrics but don’t know if a standard 13amp socket will run off the breaker safely.
Thanks in advance
 
Its fine to change the DP switch to an RCD single socket. A radial circuit off a 16A MCB.
But as others have mentioned, it will be off an off-peak board. So socket will only work between the hours of 12 midnight and 7am
 
RCD socket anyone?
Altering the purpose of the circuit though what about the method of installation ie are the cables at a sufficient depth or suitably protected against damage from nails/screws or the like do the walls have metal parts many things to consider... OP is definitely better getting a spark in...
 
Altering the purpose of the circuit though what about the method of installation ie are the cables at a sufficient depth or suitably protected against damage from nails/screws or the like do the walls have metal parts many things to consider... OP is definitely better getting a spark in...
Not at all, you are only responsible for you install or alter. So a RCD socket will comply with the regs.
 
Not at all, you are only responsible for you install or alter. So a RCD socket will comply with the regs.
Edit - worded my point better
Yeah the RCD socket will comply for the requirements for all socket outlets to have RCD protection but as you were the last to touch the circuit I think the Derry would fall with you saying that it’s safe for continued use even though the requirements for RCD protection haven’t been met though could smack an RCD spur at the board and then it would comply without having to change the board...
 
Last edited:
Don’t know if I agree with that viewpoint to be honest I know where your coming from and it probably should be the way it works but I’ve got a feeling that you changing purpose of the circuit and adding a socket to it you should ideally bring the entire circuit up to standard after all you were the last to touch it?
Where have you obtained that snippet of rubbish from?
 

Reply to 13amp socket for old storage heater in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I recently got my flat rewired. It had old storage heaters and we plan on putting modern storage heaters in. The way the electrician did the...
Replies
3
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
176
Hi all, I'm looking for a bit of assistance please from those that know more about this stuff than I do. Currently in a rented flat and there's...
Replies
10
Views
2K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock