Search for tools and product advice,

Discuss 14 new 9.5kw showers to be installed on existing supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

sparky351355

Got a job to install 14 x 9.5kw showers in a large property. There is an existing 100a 3phase supply, I've load tested the existing load and its generally pulling around 35A per phase with one only pulling around 10A (bit of a imbalance there. )I've worked out new load with diversity applied for the new showers but just after some numbers from some fellow tradesmen as there may be a couple of ways to determine the load, as a mains upgrade is on the cards and I want to make sure I'm not way off!!!!.
 
go for power showers. 14 instantaneous showers is ludicrous.
 
What kind of property is it? I'm assuming its a load of flats or a hotel/guesthouse kind of thing?

When you say you've measured the current load was this a proper load survey conducted over a week or so, or was it sticking a clamp meter on it?
 
Power showers are a no go, believe me I've asked! The property is a sheltered accommodation ,it's two large houses knocked into one, as far as the load test is concerned I'm afraid it was the latter however there cannot be a great fluctuation on the load as there is no major appliances apart from a single phase extract hood , although probably a good 20a worth and the odd kettle/2kw heater, all cookers are gas and gas central heating.
 
Ok, is this 14 seperate bathrooms?

What is the expected use pattern? Do the residents follow a set routine of any sort? If everyone is likely to be using the showers all at the same time you're probably just a little bit buggered!

If they have gas fired central heating then there could be the possibility of them having one or more big mains pressure invented hot water cylinders which could supply regular thermostatic mixer showers.
 
cut the accomodation to 13. in the spare room fit a humungous communal bath. boil up a few kettles.
 
As far as the current load goes, it's going to be much worse in winter!

Assuming 14 showers = 14 accommodation units of some form then you may be looking at 14 x 2KW heaters come winter time.

Depending on the actual people living there and the various rules about these things you may have to consider the requirements for limiting the max temperature of the water from the showers.
 
Ok, is this 14 seperate bathrooms?

What is the expected use pattern? Do the residents follow a set routine of any sort? If everyone is likely to be using the showers all at the same time you're probably just a little bit buggered!

If they have gas fired central heating then there could be the possibility of them having one or more big mains pressure invented hot water cylinders which could supply regular thermostatic mixer showers.

unfortunately I would Imagine a general rule would apply with showering , morning and night but these tenants do not work so I would imagine showering would be staggered. My question is really is wether the diversity would be applied by adding the total new load together or wether to apply as they are split across the phases as the reading is significantly different, any views?
 
You can't base anything on the load you measured as this measurement was only at a particular moment in time when you had the clamp meter on there. That doesn't give an accurate assessment of average or peak loads.

I would suggest you can't just assume showering times will be staggered, it will depend on the type of people in the sheltered accomodation. If they are people who have become institutionalised over their lives for whatever reason they may very well all follow the same routine either by accident or design.
 
You can't base anything on the load you measured as this measurement was only at a particular moment in time when you had the clamp meter on there. That doesn't give an accurate assessment of average or peak loads.

I would suggest you can't just assume showering times will be staggered, it will depend on the type of people in the sheltered accomodation. If they are people who have become institutionalised over their lives for whatever reason they may very well all follow the same routine either by accident or design.

Again true dave what I'm after here tho is as I said what load what you put for the new showers per phase?
 
I can't honestly say what I would put as the load per phase at the moment. I was taught a very old fashioned idea when dealing with 3 phases supplying single phase loads, basically keeping circuits on different phases separated, ie all simultaneously accessible sockets and lights on the same phase whilst still maintaining good phase balanceing.

So I would want to know which phase the wiring in each bathroom was connected to before deciding how many end up on each phase, and of course an accurate view of the existing loading and phase balance.
 
I've seen it quite a few places where certain room or area is all on 1 specific phase.

what about priority switching on a bigger scale
 
I would honestly push for a different solution. 14 x 9.5kw showers is not the way forward. I would struggle to apply diversity here as well, who's to say the showers won't be used all at once, ok maybe not now but in the future? At the very least, why not look at 7.5kw showers for a start! What's the need for 9.5's? ;)
 
I am planning to split the load over 3 phases fed from a consumer unit on each floor via main dis board, the rooms don't have there own c/us so this makes thing a little simpler, diversity as follows:-

14 x 9500=133000
133000/3
44,330/230=192A

div=
2 x100% + 3x25%
 
Good luck with your sub mains and ct's etc for that lot. Sounds absolutely crazy what you are trying to do.
 
I wouldn't even consider it. And you say that the water supply isn't your concern but it would be when the showers don't work due to lack of pressure........wouldn't it? I've seen this happen with only two showers in use!
 
I remember doing a washing facilities at caravan park , probsly 10 power showers were used and had a tank out back 4 times size of oil tank.. And massive pump buried out the back........ Mechanical
 
Might be worth me raising a concern over the water issue agreed! However i will have 375 A to play with here I'm sure a supply of that size and I'm sure the chances of even 50% of the showers being on at the same time ( even assuming that the the shower is at full wack(9.5kw)) this is manageable , when all that we have is low energy communal lighting and a couple of t.v.s running.
 
install a 10KVA generator (2 stroke) outside each shower room. not only will that sort out the loading problem, but starting the buggers with the pull cords will keep the old buggers fit.
 
You calculation in post number 22 was:

14 x 9500=133000
133000/3
44,330/230=192A

You added up the total KW of 14 showers then divided by 3 and calculated the per phase current from that. To achieve this in the real world you will have to connect 4.66 showers to each phase.
 
You calculation in post number 22 was:

14 x 9500=133000
133000/3
44,330/230=192A

You added up the total KW of 14 showers then divided by 3 and calculated the per phase current from that. To achieve this in the real world you will have to connect 4.66 showers to each phase.

easy when you've cut out the cable entry and wet-pants has butchered out his pipe entry then melted away half the plastic casing with his blowlamp, that's 0.34 of the 5 showers gone, leaving 4,66.
 
Might be worth me raising a concern over the water issue agreed! However i will have 375 A to play with here I'm sure a supply of that size and I'm sure the chances of even 50% of the showers being on at the same time ( even assuming that the the shower is at full wack(9.5kw)) this is manageable , when all that we have is low energy communal lighting and a couple of t.v.s running.

Unless switched to "economy mode", which nobody does, these showers always pull "full wack".
 
I think that many instant shower units is a crazy idea. You could run just 3 x 200 litre 4kW hot water cylinders, one on each phase with 5 or 6 showers piped from each cylinder. It would probably cost a fraction of the price and would draw a fraction of the peak load.
 
Ok i'll play the game here.

Assuming they are split as equally as possible (5,5,4) and as you used 230V in your earlier calculation i'll assume they are rated 9.5KW at 230V.

Total connected load on L1 = 5 * 9.5KW = 47.5kW = 197.9A

Allowable diversity if you consider thsi to be a boarding house = 100% FLC of largest 2 appliances + 25% FLC of all other appliances
Current for 1 * 9.5KW unit = 39.6A
Load after diversity = (2*39.6)+(3*(39.6/4)) = 79.2 + 29.7 = 108.9A

However you could consider these to be individual dwellings in a block then you take 100% FLC of the shower in each dwelling so we get back to 197.9A.

Either way that's going to be a bit much for your existing 100A supply
 
Why not?

Guidance note 1 table H.2 lists diversity for Water-heaters (instantaneous type) as 100% f.l. of largest appliance + 100% f.l. of 2nd largest appliance + 25% f.l. of remaining appliances.
 
Why not?

Guidance note 1 table H.2 lists diversity for Water-heaters (instantaneous type) as 100% f.l. of largest appliance + 100% f.l. of 2nd largest appliance + 25% f.l. of remaining appliances.

So does the OSG , it's thermostatically controlled that no diversity is allowed.
 
Yes but with the load after diversity being more than the existing incoming supply (100A TP) without even considering the existing load I kind of assumed that conversation would be happening anyway.
 
Yes but with the load after diversity being more than the existing incoming supply (100A TP) without even considering the existing load I kind of assumed that conversation would be happening anyway.

Fair enough , I confess to not reading the whole thread ,it was just something niggling in my mind that you had to notify them of additions over a certain level.
 

Reply to 14 new 9.5kw showers to be installed on existing supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I'm fitting one of the Apex 7S units on Friday. I'd avoided the original range after a couple of bad experiences but I figured a new model might...
Replies
6
Views
846
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
750
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock