Job today to change out old fusebox and I'd noted the 16mm tails but on pulling the fuse this morning it was 100A which I wasn't expecting. Fairly recent new smart meter installed by XYZ who are also the DNO ... Shouldn't the fuse be limited to 60A in this case? Thoughts and advice appreciated :)
 
As it's existing are you expecting that your total demand is going to be higher than the rated CCC of the tails ?
16mm tails are good for 87amps clipped direct
 
Between meters and service terminal blocks they are, as soon as you contain them they are no longer clipped direct throughout and that rating will not apply.
 
What are they rated at once you enclose them in CU as they are no longer clipped direct and should be derated.
Do you really think that Westy, really or is there some pedantry going on- you've brought it up in the past?
 
Back on track - how difficult would it be to change the tails?

What do you estimate the maximum load to be for the property? If its well under 87 amps you could reasonably leave the 16mm in place ....

tin hat is on!
 
Its all about how the cable is installed and it's ability to dissipate heat.
Sorry but that's just another post meant quite frankly to annoy people
Quite the opposite it is a reasoned argument using as you say, how the cable is installed and it's ability to dissipate heat whereby this ability is lowered once contained.
 
If a cable passed directly through a insulation packed 4x2 stud partition so that those few inches were all that was not clipped direct,how many of you would de rate the cable?
Getting rid of that heat is what the ccc are all about as Ian mentioned previously
 
Well, I did try to move the tails but only got the 20cm I needed for the new CU and they won't budge any more, although there is slack at the meter. So changing the tails will be mission messy. Tails leave the external chest high meterbox in a cavity brick wall, go up and over the front door and drop down from the ceiling. CU mounted high up next to ceiling behind front door. New CU is in the location of the original fuse unit, at Customer's request. But somewhere in that lot the tails go through a beam I reckon and are jamming up. Nothing I can't sort if I rip into the plaster ceiling she's just had done :( .

In terms of load, I am sure a 60A fuse would be fine. 2BR mid terrace, newish combi for CH and HW. Biggest drain will be an induction hob she's got on order.

There's no insulation anywhere near the tails that I can see looking from both ends. The tails will be less than 3m long.
 
Well, I did try to move the tails but only got the 20cm I needed for the new CU and they won't budge any more, although there is slack at the meter. So changing the tails will be mission messy. Tails leave the external meterbox in a cavity brick wall, go up and over the front door and drop down from the ceiling. CU mounted high up next to ceiling behind front door. New CU is in the location of the original fuse unit, at Customer's request. But somewhere in that lot the tails go through a beam I reckon and are jamming up. Nothing I can't sort if I rip into the plaster ceiling she's just had done :( .

In terms of load, I am sure a 60A fuse would be fine. 2BR mid terrace, newish combi for CH and HW. Biggest drain will be an induction hob she's got on order.

There's no insulation anywhere near the tails that I can see looking from both ends. The tails will be less than 3m long.
As long as regulation 434.5.2 is met for protection of the tails for fault current and your total load profile taking into account diversity is not going to overload the CCC of the tails you will be fine.
 
Of course the DNO may stipulate a maximum CSA of bigger than 16mm tails if connecting directly into their equipment.
Of course we all ring them all the time to enquire don't we?:)
Yes, what was the DNO thinking putting 100A fuse in and saying nothing to owner (she's lived there forever) about the 16mm tails... and the DNOs smart meter guy ...
 
As long as regulation 434.5.2 is met for protection of the tails for fault current and your total load profile taking into account diversity is not going to overload the CCC of the tails you will be fine.
Got the books out, calculator valves just warming up.
 
New posts

Reply to 16mm tails with 100A fuse ??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
678
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
811
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock