Discuss 19 Flats fed via Mccb/ryefield.........isolaters?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all,
I am currently in the process of quoting a job to renew the mains for 19 flats. This is the first job of this type that I have quoted so just after a bit of advice.
The flats are currently supplied via a ryefield panel in mains room which supply's a further 4 ryefield panels in risers. If I were to replace the ryefield in mains room to a new mccb panel to then supply ryefields in risers would I then have to install switch fuse isolaters after ryefield? Thanks
 
Not absolutely sure I'm following you. I would have thought the riser Ryefields are still fused panels with isolation at distributed points.
 
I also don't see the need for switch-fuses after the Ryefield - typically each flat will have a cut-out with a solid link for local (i.e. sparky working in anyone's flat) isolation and the design ought to be such that the Ryefield's fuse can protect cables to that point. Ideally they would have isolation switches after the billing meters but we know that is not always the case :(

What I am not clear about is if they have to follow 5 sec distribution circuit ADS per wiring regs that sparks follow, or if they fall under DNO regs where it is simply overload protection of the network?

As for replacing the Ryefield at the origin with a MCCB panel that is up to you. If there is any need for a non-skilled person to be able to isolate or reset then MCCB fit the bill, but otherwise fused Ryefield along with some incoming isolator switch is likely cheaper and provide better fault selectivity if you have at least a 1.6:1 ratio. E.g. With 19 flats and 4 sub-Ryefield it looks like 5 flats per board, so about two per phase. They are probably on 60A fuses (any info on per-flat demand estimate?) so if the source Ryefield is using at least 100A fuses then total selectivity is possible and probably fine for diversity of loads.

Same for those and the incomer, if the DNO incomer is at least 160A fuse per phase then you ought to have total selectivity with the first board at 100A, etc.
 

Reply to 19 Flats fed via Mccb/ryefield.........isolaters?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hello, I’m about to take on a mains room for a block of flats and the DNO are giving us a supply of 259kva. Now, would I need a 200amp TP-N...
Replies
3
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock