Discuss 3 36kw cookers in cafe in the Commercial Electrical Advice area at ElectriciansForums.net

R & S

-
Reaction score
0
Hi, been asked to install 3x 36 kW 53A ovens and 9 kW 3 phase dishwasher in a cafe 100a 3 phase supply. I think the best way is to have 2 ovens on a change over switch so only 2 can run at once, but he wants all 3 but I think it will be to expensive to upgrade. What does everyone think
Thanks for help
 
allowing for diversity,ovens will be switching on and off due to thermostats. should be OK. try switching each one on in turn and clamping the supply tails.
 
Hi, been asked to install 3x 36 kW 53A ovens and 9 kW 3 phase dishwasher in a cafe 100a 3 phase supply. I think the best way is to have 2 ovens on a change over switch so only 2 can run at once, but he wants all 3 but I think it will be to expensive to upgrade. What does everyone think
Thanks for help
36kW is a hell of a big oven. Are these cookers, with rings on top?
 
36kW over 3 phases is 53A/phase approx, so a 100A/phase supply will be adequate, depending on what other loads will be in use.
 
They are pizza ovens, that's what I work out 53a each phase there is not much else in there I thought it would be pushing it have all 3, in case all come on together
 
Hi dude,seems strange that an operation with three of those ogres,would not have requirements for heating,lighting,washing,ventilation,warming and a phone charger ;)
 
They are pizza ovens, that's what I work out 53a each phase there is not much else in there I thought it would be pushing it have all 3, in case all come on together

You think it would be pushing it?
How about some calculated values rather than an 'I think it would be' kind of guesstimate?

What diversity factor have you established for this?
 
Nothing else big in there at moment just display chiller units, no vents and small water heater for sinks. The ovens I worked out using 100% for 1st then 80 and 60 which is over the 100a supply without anything else
 
His going for just 2 at moment, very little else in there gas for water, small vent. So cookers will be 93A for 2 (100% + 80%) . Not worked in many restaurants what's everyone opinions. His hoping to upgrade later on to 200A
 
They are 3 phase 36kw / 53A per phase, there is 8kw 3p dishwasher, 15 ceiling panel lights and sockets for display chiller units and fridge and freezers
 

Reply to 3 36kw cookers in cafe in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I'd appreciate a quick sanity check, thanks in advance: New circuit for a 3 phase cooker, in a community centre (run by a charity). Total load...
Replies
2
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
616
How can I convert a 3-phase (220 volt 5.6 kw) pizza oven to 1-phase (220) 2 heating elements, no motor.
Replies
4
Views
1K
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
721
Hi, we are converting old farm buildings to commercial units, and as my father used to run a vacuum pump and compressor in his dairy I always...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock