Discuss 3/4 Outlets No longer working in same room in the UK Electrical Forum area at ElectriciansForums.net

Georgee

DIY
Reaction score
0
Last night, all of my outlets in my family room were working just fine. This morning, however, I discovered all the outlets that had something plugged in no longer work. I checked the breakers and all is fine. It’s just odd the one outlet that doesn’t have anything still works. We did have a couple storms roll through but that was all while I was watching TV and it was working. The TV is on a surge protector but the others were not. What could the problem be?
 
All the breakers are on and staying on, yes? Do any of the affected outlets contain a GFCI, and if so, do the test and reset buttons work? Are there any GFCI outlets nearby* that might have tripped, but not been noticed?

If nothing is tripped then it is quite likely that there is a failed connection at the first outlet along the circuit that doesn't work, or the last one that does. The fact that the outlet that is still operational didn't have anything plugged in at the time, may be just a coincidence.

*UK readers note that the OP is in the US, where GFCI receptacles have extra terminals on the load side of the GFCI that can be used to protect ordinary outlets downstream. Therefore one tripped GFCI point that may not itself have been in use, can disable multiple other points.
 

Reply to 3/4 Outlets No longer working in same room in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
477
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Replies
9
Views
814
Our family room is part of an addition built a few years ago. We had an issue with nuisance tripping on an AFCI and the electrician came and...
Replies
2
Views
1K
A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
570

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock