Hello,

New here, but hopefully someone can help...!

We have been tasked with installing a number of very small pumps (21 in total) on a large site. Running individual cables to the 7 areas (3 x 1.0kW / 400V / 3phase / DO.L. pumps in each area) where these pumps are located would be expensive.

I would like to install a 3-phase & neutral ring main but I'm unsure how to calculate this for volt drop / current carrying capacity. If I were to proceed this way the end to end (circular) length of the ring would be around 2000 metres...

Any suggestions?

Cheers, Sumo
 
2km ring main! is this correct?

What are the pumps doing?
Will they all come on together?
Any other power requirements in the same areas for lighting, power etc even if only for maintenance reasons?
Any equipotential bonding requirements where these pumps are situed'?


Before advising we need to get as much info as possible to avoid wrong advice due to lack of info.

Lastly what is your experience in this field and what is your normal working environment so as to tailor our advice.

Lastly again welcome to the forum.
 
Last edited:
Also why do you need a neutral? For the length of run your suggesting a small 400 - 230 tx in each panel will be cheaper than 2km of an extra core.
 
Hello,

New here, but hopefully someone can help...!

We have been tasked with installing a number of very small pumps (21 in total) on a large site. Running individual cables to the 7 areas (3 x 1.0kW / 400V / 3phase / DO.L. pumps in each area) where these pumps are located would be expensive.

I would like to install a 3-phase & neutral ring main but I'm unsure how to calculate this for volt drop / current carrying capacity. If I were to proceed this way the end to end (circular) length of the ring would be around 2000 metres...

Any suggestions?

Cheers, Sumo

You real or just extracting the urine?
 
I'd be interested to know why you think a ring main would be the best method of distribution.
 
Basically, it's a large quarry (hence the 2000m run if we did it as a ring) where there are 21 dewatering wells currently being drilled. There are 7 different locations, each location having 3 wells. We plan to install borehole pumps and install a small 4-way (3ph) DB at each of the 7 locations, these DB's in turn feeding 3 local DOL pump panel.

We normally run radial feeds to pump panels / DB's... However, the customer wants to keep costs to a minimum and I hope a ring main may do that.

The alternative is a huge radial which would be around 1600m in length to pick up the 7 separate locations.

As the pumps will be controlled individually via pressure transducers it is possible (however unlikely) that they could all start at he same time. Pumps range from 0.5kW (15 pumps) to 1.1kW (6 pumps)

Many thanks
 
string some 11kV round on poles and transform down at each location. :ack2:
 

Reply to 3-Phase / 400V ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
985
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
993
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top