Discuss 3 Phase Calculations for Star and Delta in the Commercial Electrical Advice area at ElectriciansForums.net

T

TailSpin

Hi All

just a question for the more mathematical people.

Have got three 15kw water heaters wired in Star . What is the current calculation for this per phase and would this change if wired in delta assuming a pf of 1 ?

Regards

John :6::rolleyes2:
 
If you're wiring in star you will have 230v rate heaters assuming mains voltage if you wire in delta you'll have no heaters left assuming 400v across phases.
 
While you're checking the voltage, have a look if there's a neutral to the start point. If there isn't there's all sorts of fun calculations for you to do.
If they turn out to be 230V please don't atempt to connect them in delta. (Seen it done in a gearbox oil heater. Cost £1000's to put right).
 
Current in star (Ip=IL)=15Kw/((√3)x400x1)=21.6A
Line Current in Delta IL=15kw//((√3)x400x1)=21.6A
Phase Current in Delta Ip=21.6A/(√3)=12.5A

Lucky its balanced

(Pf would be 1 on a resistive load)
 
As a hint, you have to calculate the resistance of each element and then transpose the higher voltage due to them being connected in delta.
The reason I asked if there was a neutral, if one fuse blows it chucks a real spanner in the works.
 
As a hint, you have to calculate the resistance of each element and then transpose the higher voltage due to them being connected in delta.
The reason I asked if there was a neutral, if one fuse blows it chucks a real spanner in the works.

LOL Sorry, i took a red face for that, ignore that calc, give me 10 mins
 
How about this one

Current in star (Ip=IL)=45Kw/((√3)x400x1)=65A
Line Current in Delta Ip =45kw/((√3)x400x1)=65A
Phase Current in Delta IL=65Ax√3=113A
 
Last edited by a moderator:

Reply to 3 Phase Calculations for Star and Delta in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
659
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
879
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock