Discuss 3 phase domestic job in the Commercial Electrical Advice area at ElectriciansForums.net

Why would you want to put an rcd of any type on a distribution circuit ?
To work out diversity it would be best to start with total connected loads allowing a sensible amount for socket circuits. Load division across phases also needs balancing as best as possible.
The electric heating plan sounds very costly to run. Have they no gas ?

The T&E distribution runs through the walls of the house. I can't see it. So I guess that is why?

Yes, it is costly and no, they don't have gas. Out in the countryside!
 
Currently the


No, even I know that is a bad idea they are all on separate mcbs, currently distributed across the three phases and I would maintain that. I was considering the merit of splitting the three phases by location as that suggested or whether I run all three phases to both locations to aid balancing and possibly flexibility.

Sorry if my explanation and choice of words isn't clear.
Is it possible to install a poly phase DB, as opposed to three separate SP DBs? the poly phase way allows you to split the loads in a more beneficial way, imo
 
I hadn't thought too much about the current installation as I am essentially starting again but having been asked about the RCD and thought about it, the current 3ph feed from the RCD is off peak only and only powers the heaters which are on mcb. The RCD near the origin provides additional protection to all the heating radial circuits.
 
If they are out in the sticks try selling them a ground source heat pump and thermal store for most of their heat. Ground Source Heat Pumps | GSHPA is the focal point of the ground source heat pump industry | Renewable Heat | Renewable Cooling | GSHP | Ground Source Heat Pump Systems - https://www.gshp.org.uk/ as for the distribution side, I would suggest make provison for 3 phase distributon to any garrage so if need be they can install pumps and so on.

As for the heating, ask can their improve the insulation, improve the controls, and tactfully suggest they need to think like what it was like before central heating, in other words in a big house you made one room tosty warm and the others were cooler.

Other ways also look at all loads that could be run off E7 / E10 The supplier should provide a time clock, or radio switch, both can appear to "drift". To make sure the switching is done at the correct time for loads which are remote, use a 6A MCB on the offpeak board to control remote contactors fed from the 24Hr supply, that way you only need to supply an extra 1.5mm T+E but mark up the contactor enclosure dual supply! or use a 240V to 24V transformer and 24V contactor coils subject to voltage drop.
 
If they are out in the sticks try selling them a ground source heat pump and thermal store for most of their heat. Ground Source Heat Pumps | GSHPA is the focal point of the ground source heat pump industry | Renewable Heat | Renewable Cooling | GSHP | Ground Source Heat Pump Systems - https://www.gshp.org.uk/ as for the distribution side, I would suggest make provison for 3 phase distributon to any garrage so if need be they can install pumps and so on.

As for the heating, ask can their improve the insulation, improve the controls, and tactfully suggest they need to think like what it was like before central heating, in other words in a big house you made one room tosty warm and the others were cooler.

Other ways also look at all loads that could be run off E7 / E10 The supplier should provide a time clock, or radio switch, both can appear to "drift". To make sure the switching is done at the correct time for loads which are remote, use a 6A MCB on the offpeak board to control remote contactors fed from the 24Hr supply, that way you only need to supply an extra 1.5mm T+E but mark up the contactor enclosure dual supply! or use a 240V to 24V transformer and 24V contactor coils subject to voltage drop.

Thanks. Will look into GSHP. Potentially a good idea.
 
Is it possible to install a poly phase DB, as opposed to three separate SP DBs? the poly phase way allows you to split the loads in a more beneficial way, imo

I believe I could do either. I was hoping for help deciding which was the better method. Sounds like you agree that it is worth running 3 phase to both locations for the benefit of the flexibility. When you say a Polyphase board, is that different from a 3phase board? If so, can you give me a link to an example? Thanks.
 
I believe I could do either. I was hoping for help deciding which was the better method. Sounds like you agree that it is worth running 3 phase to both locations for the benefit of the flexibility. When you say a Polyphase board, is that different from a 3phase board? If so, can you give me a link to an example? Thanks.
Poly phase is a posh way of saying 3 phase, no I dont mean take 3 phase to each location, what I mean is have 1 3phase DB so you can ballance the SP loads more easily at one point of connection, taking 3 phase to different locations will mean running sub mains to each position, sounds like my 1st suggestion is a non starter on this occasion.
 
I believe I could do either. I was hoping for help deciding which was the better method. Sounds like you agree that it is worth running 3 phase to both locations for the benefit of the flexibility. When you say a Polyphase board, is that different from a 3phase board? If so, can you give me a link to an example? Thanks.
Poly phase is a posh way of saying 3 phase, no I dont mean take 3 phase to each location, what I mean is have 1 3phase DB so you can ballance the SP loads more easily at one point of connection, taking 3 phase to different locations will mean running sub mains to each position, sounds like my 1st suggestion is a non starter on this occasion.
 
Poly phase is a posh way of saying 3 phase, no I dont mean take 3 phase to each location, what I mean is have 1 3phase DB so you can ballance the SP loads more easily at one point of connection, taking 3 phase to different locations will mean running sub mains to each position, sounds like my 1st suggestion is a non starter on this occasion.
In my opinion the best and easiest way would be to have one central DB, this will allow you to, balance the loads easier, save you money by not having to run sub mains to remote locations, the only difficulty I can foresee is being able to extend the final circuits to the central DB, but without eyes on it's difficult to give any practical advice.
 
Yes, that us definitely an option. No 3ph equipment.
Some hobs have the ability to connect to two phases of a 3ph supply. Might be useful to help spread the load as the hob is going to be one of the highest power consumers.

But I'm not based in the UK, different rules and different gear in the shops. My hob is AEG.
 
I presume the 'Dumb' rating in my post #2 is by accident @stevels4 ??
:):)
 
This could be a good opportunity to simplify everything and tidy it up a bit - unless there's a good reason for them I'd put everything from those 3x single phase consumer units together in one 3 phase board on RCBOs.

Depending on the layout it may be worth taking sub mains to different parts of the house, but just because they don't currently own any 3 phase equipment doesn't mean they're not going to suddenly decide to make the most of their 3 phase supply, go out and buy a 3 phase pizza oven or welding set, you know, because they can.
 

Depending on the layout it may be worth taking sub mains to different parts of the house, but just because they don't currently own any 3 phase equipment doesn't mean they're not going to suddenly decide to make the most of their 3 phase supply, go out and buy a 3 phase pizza oven or welding set, you know, because they can.

They may even decide to have a stage the garden and host a mini festival!
 

Reply to 3 phase domestic job in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
652
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock