how about using 10A 3 pole pole mcb's each feeding one contactor this gives 10 * 230V = 2300 W per phase
divide this by 1.8 correction factor gives 1278 watts per phas divide this by 250w (perlamp) = 5 fitting per phase 15 per contactor. This means only 4 contactors for 60 fittings.
split the fittings into banks and you will only lose a quarter of all the fittings if an mcb trips
Thats exactly what I was thinking but usings4 pole contactors. Excellent idea about the 3 pole MCB to cover but I was thinking 25amp.
Take a look at the diagram that I'm posting and let me know what you think. Should I have a 4 pole MCB for the 3 phase or 3 individual fuses??.
regards