Hi, Does anybody know of any alternative to governing the speed of a 3 phase motor than a frequency inverter? Thanks in advance, Jamie
 
I guess if it doesnt involve T+E you fellas are banging your head against the wall, thanks for the comedic replies though, just amazing....
 
I guess if it doesnt involve T+E you fellas are banging your head against the wall, thanks for the comedic replies though, just amazing....

If it,s a "bog standard" asynchronous induction motor (most common 3-phase motor) your meaning, a frequency converter is the only practical method. There is other more specialist 3 phase motors that can be controlled by other means but these are not very commonly used. Frequency converters are by far the most common way of controlling the speed of an AC 3 phase motor.
Noticed you got some really,really funny replies. Lol
 
Last edited:
If it,s a "bog standard" asynchronous induction motor (most common 3-phase motor) your meaning, a frequency converter is the only practical method. There is other more specialist 3 phase motors that can be controlled by other means but these are not very commonly used. Frequency converters are by far the most common way of controlling the speed of an AC 3 phase motor.

Thanks, yes this is what I thought was the case, i am thinking that the frequency inverter can be controlled via a panel mounted potentiometer
 
You can control them via a potentiometer yes but depending on the make/model you can get a range of operator panels to give them better control and feedback on key parameters. Is the motor existing or to be sourced?
 
You can control them via a potentiometer yes but depending on the make/model you can get a range of operator panels to give them better control and feedback on key parameters. Is the motor existing or to be sourced?

The motor is already in place D.O.L. , the budget is the main issue here, I wouldnt think that there will be any need for feedback or any kind of ramping up/down of speeds, just a means of governing the speed of the bandsaw blade for cutting different materials
 
Thanks, yes this is what I thought was the case, i am thinking that the frequency inverter can be controlled via a panel mounted potentiometer

Yes it can easily be controlled via a potentiometer and since the motor you want to speed control seems pretty small, and budget is important to you, I would think it would not cost more than a couple of hundred pounds to source a suitable VSD.
 
Yes it can easily be controlled via a potentiometer and since the motor you want to speed control seems pretty small, it would not cost more than a couple of hundred pounds to source/install

Thanks for all the advice, do you have any recommendations for a frequency inverter to use for this application @ 1.1KW
 
It depends on the reputation/support you want from the manufacturer. We use both ABB and Danfoss inverters depending on the customer.
 
Yes, I have had some involvement with both ABB and mitsubishi AC Inverters, as this job is on a tight budget I was hoping that somebody may have a cost effective solution with regards to a cheap no frills inverter, thanks again
 
The motor is already in place D.O.L. , the budget is the main issue here, I wouldnt think that there will be any need for feedback or any kind of ramping up/down of speeds, just a means of governing the speed of the bandsaw blade for cutting different materials

Hold it right there!

Have you spoken to the manufacturers about this. You're entering a legal nightmare.
 

Reply to 3 Phase Motors Speed Control in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
804
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
344
Hi all I just picked up an older 36 volt golf cart The speed controller is a curtis 36volt 350 amp I was wondering is there a way of protecting...
Replies
2
Views
635
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock