Discuss 3 phase sub board addition in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Hi

Looking at a job currently adding a 3 phase solar installation but the distribution board is full obviously a new board is the best option but if the customer isn't interested in this what do people usually do? Add a small 3 phase board and use Henley blocks, I've never seen this done but I don't do much 3 phase work.

Any better options?

cheers
 
What size installation are we talking about here?
Is it just a small 100A supply with tails directly feeding a single DB or is it a big installation with a busbar you can tap off for a new feed?

How many new circuits are you installing?
If its just one circuit and there's a busbar available then you could add a switchfuse to it for the new circuit.

Another option is to fit a second DB next to the existing one and move an existing circuit (or 3) into it to free up a way to feed the new DB from that.
 
What size installation are we talking about here?
Is it just a small 100A supply with tails directly feeding a single DB or is it a big installation with a busbar you can tap off for a new feed?

How many new circuits are you installing?
If its just one circuit and there's a busbar available then you could add a switchfuse to it for the new circuit.

Another option is to fit a second DB next to the existing one and move an existing circuit (or 3) into it to free up a way to feed the new DB from that.
Its a small 100a 3 phase installation. Your last option could work well, add a small single phase board and move some of the lighting over to that. This would allow me to add one 3 phase mcb for my inverter.

cheers
 
Its a small 100a 3 phase installation. Your last option could work well, add a small single phase board and move some of the lighting over to that. This would allow me to add one 3 phase mcb for my inverter.

cheers

Do the next person a favour and put a 3 phase board in so theres a few 3 phase ways spare for future expansion.


And I know this is obvious but try to use the same brand of DB as the existing.
 
What make/age is the existing board?

A few like Hager offer 'neutral links' which are dummy MCB with just a link and they can be used to extend the busbar of the main board to a new one so no additional main switch needed and no selectivity issues of MCB feeding MCB. Obviously you have to be within overall current limits, etc, and as no final circuit protection on those linking cables they need to be double-sheathed (like tails) or ideally just box-box via trunking or a 32mm or 50mm bush and locknut physically linking the two DB together.
 
That’s the preferred option but I’m not sure the customer will go for that.

Cheers
So they are adding quite a lot of panels, a 3 phase solar inverter and are going to turn down 2K to put a decent board in and install it properly?

put in the quote for doing the job you feel should be done.
if they grumble, then you can say
it can be done on the cheep like this but i wouldn't recommend it.
 
So they are adding quite a lot of panels, a 3 phase solar inverter and are going to turn down 2K to put a decent board in and install it properly?

put in the quote for doing the job you feel should be done.
if they grumble, then you can say
it can be done on the cheep like this but i wouldn't recommend it.
I agree but often people aren't keen on a new board as that's not what they have asked for hence lots of domestic installs have a separate small board for the Solar. I was just wondering what people often in that situation.
 
I agree but often people aren't keen on a new board as that's not what they have asked for hence lots of domestic installs have a separate small board for the Solar.

Is that the reason? Or is it because of some solar installers who only care about doing the quickest, cheapest job and getting on to the next one?
 
Is that the reason? Or is it because of some solar installers who only care about doing the quickest, cheapest job and getting on to the next one?
Funny how views differ most people I know regard it as best practice to keep solar in a separate board and using the existing board is a Last resort.

I always want to do a decent job, if you add a full board change, which to do properly is a full day to every job you wouldn’t get the jobs.
 

Reply to 3 phase sub board addition in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
954
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
283
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
482
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
I didn't get a picture so will have to wait until I go back again but I've done a crude drawing of what was there. Its in a commercial set up...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock