Is there an existing distribution board in the new building?
No its a new building, there was a mobile unit there a few years ago but there was just a cable left over. This building is meant to be more permenant. The cable was just disconnected in the main building DB. It runs under a playground so theres no chance of running a new one or thats the route i would have gone. I've been asked to reinstate the cable and fit a new DB plus a few sockets, lights and water heater for the toilet.
 
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.
 
Thats the one mate. The earth strap in these kits cant have the same CSA as the armour so i didnt want to use it as a main earth. Its a resin joint.

The CSA of the tinned copper braid is different to that of the armour, copper has a much higher conductivity so you need far less of it to get the same current carrying capacity.
If a correctly sized joint kit has been used then I see no reason to worry, it has been designed for this purpose.

There is no seperate CPC. The SWA is earthed but i wasnt confident in using this as a main earth for the installtion of the building because of the join.

If you are concerned that there is a problem with the joint cut it out and re-joint the cable properly.
 

Reply to 3 phase supply to classroom, unsure to TT? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
607
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
657
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
I have a single phase stainless steel pasteuriser that has two control boxes attached to it. One box houses the control for the electronics and...
Replies
2
Views
684
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
872

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock