Search the forum,

Discuss 3 phase supply to communal shower block in the UK Electrical Forum area at ElectriciansForums.net

B

bobbert

Hi Guys,

Looking for a little advise regarding installation of new supply to feed a communal shower block at a local Girl Guides Camp.
The owners have just had the supply upgraded from single phase to 3 phase on my advise as their new power requirements are now much greater with the arrival of their shower block.

The shower block is a porter-cabin type of affair with 4 8.5Kw electric showers, 3 3Kw over-sink instantaneous water heaters, a couple of frost guard heaters and lighting with a couple of extractors. In total i calculate the max load to be just shy of 44.5Kw.

The shower block came from an industrial site and is currently wired as single phase feeding 2 CUs.
I'm proposing to run 3 phase to the shower block, add a third CU and juggle the loads equally across the 3 boards.

Given the loading I'm torn between running 16mm or 25mm 4core SWA back to the supply. Any input guys? ... as looking at the big red book, 16mm would just about do it but it does cut it fine. Cable run is only 6mts and will be clipped direct.

The next problem I have is what size breaker to fit at the supply end ...
As the site has new 3 phase supply there is no existing 3phase board as yet.
I need to fit one and then run submain out to shower block.
Most standard load 3 phase boards only allow a maximum rating of 63A for the MCBs and I'm feeling that this will be too small for the shower block.

I've calculated the max load as everything on at the same time due to the fact that the shower block will be used by guides/scouts during both summer camps but more importantly WINTER Camps.
The way I see it, everybody could all turn up at once to shower/wash on a cold day so I can't really justify using diversity can I?

Based on this, I'm thinking that the submain will need to have overload protection of 80A if this is the case then I'm faced with the problem of finding a TPN board that will allow me to fit an 80A 3pole MCB.

Anyone else had this problem?
I've installed TPN boards before that have high-load outputs but these have been seriously pricey and I can see this becoming a problem.

I know that Hager do 80A 3pole MCBs but I don't know what boards they fit into.

Any suggestions on where I can find such a board without it costing the earth?
Supply to site is TT so I'll need the option of RCD main incomer too which I know most boards do now anyway.

Thanks guys ... this one has left me tied in knots :(
 
I am probably totally wrong here but with 4 x 8.5KW showers on 3 phase that's 1 shower per phase plus 1 shower. So 2 showers on 1 phase. So that's 17Kw on a single phase. As OP said can't allow for diversity as all showers might be used at same time. Am I right in assuming a 63amp mcb is capable of 14.5Kw i.e. 230x63. So a 63amp mcb is not capable of handling the load.
 
Actually i did make a mistake in my metal arithmetic on this one.... lol!!
So yes it would have to be an 80A protective device supplying this shower block...

Sorry all.... :smiley2:
 
Have you considered water pressure? We hardly get enough water pressure for 1 shower in the summer, let alone 4 and 3 wash basins, all in use at the same time.

Why not fit 7KW showers? They will also help with both power and water demand.
 
Thanks for all your advise guys!

Amazingly this place has amazing water pressure even though they are in the middle of nowhere... I think they have a water main coming from a nearby farm which I'm guessing has a some kind of pumping station.

The showers are already in situ so I can't really see them going for boiler changes.

Any ideas with regards to a board that will take an 80A 3 pole MCB ??? ... this part is giving me a headache :(

Thanks again all!
 
You won't find an MCB above 63A anywhere, you'd have to move into MCCB territory if you wanted it to be re-settable.

I haven't looked but are you allowed multiple phases in a room containing a shower?

I would suggest that you temporarily wire one of the showers up and see what load it takes, the amount of power used depends on the desired water temperature and the temperature of the incoming water.
 
Square D or Schneider as you might call it now, do a MCB board at the bottom to each side is a din rail which accommodates various equipment including a small MCCB which is sort of made for it. You then fit 1 module through connectors in place of the MCB and drop down with tails to your MCCB.

I have no details to hand but have a look at the Schneider dist boards.
 

Reply to 3 phase supply to communal shower block in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
684
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
780
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
327
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top