Discuss 3 plate wiring at switch?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

O

onamission

As a training electrician i yesterday came across, for the first time, the 3 plate wiring method wired into a switch. I was slightly confused on how to terminate this? There were 3 twin and earths present (feed in, feed out and what i assume is a switch line and neutral?) and a 3 core seeing as it was a two way switch. Any help would be appreciated because, as i said, it left me slightly confused as i had never came across this before. Thanks in advance.
 
yep, L/N in, swl/N out, 2 way switch with 3 core and L/sl. neutrals in choc block. sometimes it's easier to wire this way than llop in at the fittings. also has the advantage of a neutral at the switch position, ideal for adding things like porch lights without having a load of chasing new plaster and decoration
 
It's being done a lot more for use in mobile/park homes/caravans for example where all wiring is under floor.
Basically you loop N's when you would have looped L's at light.
Also means with a deeper switch box loads more room for looping than in fancy light fittings & the dreaded downlights.
Easier for PIR later too, N available for 'no-trip' connections
 

Reply to 3 plate wiring at switch?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
674
Hi, I'm currently in my year of my apprenticeship looking for some help with the 2 plate method (feeding the switch). I understand it up to the...
Replies
3
Views
3K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
662
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock