Discuss 3 way gang switch Led bulb still lights when switched off. in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
0
Hope someone can help, went to replace sensor bulbs (incandescent) with leds when the bulbs went off or switched off they stayed on but with a small glow. I disconnected feed to utility light and lights went off no problem reconnected problem started. Is there a way to fix this problem, thanks for any advice.
20181223_072909.jpg
 
Are you saying you replaced the bulb to led and when you put in the bulb knocked off the mcb ?
 
First off the middle switch doesn't appear to be doing anything, so assuming it was working and was actually turning something on and off, you've changed something.

If the sensor lights don't have a neutral connection on the sensor, they will be passing a small current through the sensor to drive the electronics. This is often enough to make LED bulbs glow.
 
Looking at those tails and the cpc joined together with other colours i think some thing amiss on that switch and are there any cpc to that back box .
Looks lile a diy job .
op was that wiring done by a spark ?
 
Last edited:
First off the middle switch doesn't appear to be doing anything, so assuming it was working and was actually turning something on and off, you've changed something.

If the sensor lights don't have a neutral connection on the sensor, they will be passing a small current through the sensor to drive the electronics. This is often enough to make LED bulbs glow.
Middle switch not in use just has the live coming in and feed to other switches
 
Looking at those tails and the cpc joined together i think some thing amiss on that switch and are there any cpc to that back box .
Looks lile a diy job .
op was that wiring done by a spark ?
There is an earth wired to back of box, done by a spark, the sensor switch runs in a loop with a switch from another room but that didn't effect the set up
 
Hi - on the g/y for a moment - I see there's one in the plaster on the bottom of the backbox and one in the bundle to the left. Is there a reason these are not connected together?
 
The bundle on the left look like a spare circuit, maybe going to a light that isn’t there anymore. Possibly what the middle switch once did.
There’s a cpc to the back of the box, so that’s fine.
The circuits are wired in 6181y single sheathed cables (no cpc, like meter tails but much smaller) so I suspect a joint box somewhere.

Possible the LED lamps are receiving just enough current to light up through the PIR. There may be specs on the PIR itself to what load is suitable for it. LEDs might just be too low.
 
The bundle on the left look like a spare circuit, maybe going to a light that isn’t there anymore. Possibly what the middle switch once did.
There’s a cpc to the back of the box, so that’s fine.
The circuits are wired in 6181y single sheathed cables (no cpc, like meter tails but much smaller) so I suspect a joint box somewhere.

Possible the LED lamps are receiving just enough current to light up through the PIR. There may be specs on the PIR itself to what load is suitable for it. LEDs might just be too low.
Yes bundle on left never used (outside lights). May call someone In.
 
That’s a good idea, Dennis... but be aware, make sure you get a recommended tradesman and not some cowboy that’s going to spend hours tracing cables unnecasseraly. If it works as it should with a regular lamp, but not with LED, then it’s an issue with the LED /PIR combo.
 
That’s a good idea, Dennis... but be aware, make sure you get a recommended tradesman and not some cowboy that’s going to spend hours tracing cables unnecasseraly. If it works as it should with a regular lamp, but not with LED, then it’s an issue with the LED /PIR combo.
Thanks very much
 
If you do call someone in get them to tidy up those cables there are too many cables in there for the size of the box. Where are the lugs to screw the light in to? And the live into the unused gang could go to one of the used switches and a link across to get rid of at least one cable as well as cutting back the unused outside lights.
 
Ignoring all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.

https://uk.farnell.com/roxburgh/xe1202/rc-network-250v-0-2uf-120r-pcb/dp/2336099?st=snubber
all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.
 
Ignoring all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.

https://uk.farnell.com/roxburgh/xe1202/rc-network-250v-0-2uf-120r-pcb/dp/2336099?st=snubber
all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.
 
Ignoring all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.

https://uk.farnell.com/roxburgh/xe1202/rc-network-250v-0-2uf-120r-pcb/dp/2336099?st=snubber
all the wiring in the switch (which I assume you have not altered), this is a common problem with LEDs and is due to induction between a line and switched live cable. The usual fix is to put a snubber (capacitor and resistor in series) across the LED.
 

Reply to 3 way gang switch Led bulb still lights when switched off. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi we are replacing light fittings in our home. Im confident with the fitting aspect, but have run into doubt in making the right choice of...
Replies
2
Views
490
our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
230
Hello, I've installed a Monsoon Extractor Fan kit today, all is up and running and everything is working with the exception of the LED. When I...
Replies
0
Views
707
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
628
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
204

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock